hi all i was just in the middle of doing an eicr on a caravan park and wanted some opinions on what codes are relevant to the site.

ive got tncs pme 100a 3 phase. each phase feeds a db like in the picture by a 100a main switch and 63 amp mcb and 10mm pyro (earthed with bonding clamp) which in turn feeds a static caravan by i think is 60898? 20a mcb (but could do with second opinion as im not as old as the mcbs) and 2.5 2 core swa connected directly to static home consumer unit again some earthed by bonding clamp at distribution board. no bonding at all to the chassis and no rcd except inside each static home

20180119_132736.jpg - https://drive.google.com/open?id=0BywXO5AAQnhsQkhwT002Q0NmdEpDUktXR01RVzhzZGxSVnZJ


all earth at the moment is exported from met tncs im thinking....


exported earth - c2
no rcd to each static home - c2
earth clamps on the swa c2 ( some are failing due to corrosion )
earth clamps on the pyro - c3
no extraneous bonding - c2
no earth at metal meters - c2

also these are not all defects just ones i was hoping for opinions on



ANNNDD... OPINIONS.... (plus abuse mildly welcomed !)
 
They are type 4 Federal Electric devices and you need manufacturers data to compare Zs values. Sounds like you are out of your depth on this.
 
yeah, and a c1 for the water table in the utility cupboard!
 
  • Agree
Reactions: Pete999 and ruston
Mr Rigsby ,rising damp ,came to mind!
 
  • Funny
Reactions: Pete999 and ruston
They are type 4 Federal Electric devices and you need manufacturers data to compare Zs values. Sounds like you are out of your depth on this.
To be fair I am a bit as I haven't done much work on caravan parks and this is first eicr on one
yeah, and a c1 for the water table in the utility cupboard!

As said there's more defects. I'd say c2. But it is being sorted over weekend
 
  • Like
Reactions: westward10
no earth rod near that sub mains or they using the pyro has a stake.
 
I would tell the Noah the owners ,to start bailing the ark out !
 
From your pic and what you are saying it sounds an appalling installation and you need to be very conversant with the requirements to compile a concise and factual Report. Do you have GN8.
 
  • Agree
Reactions: Pete999 and ruston
op ,page GN8 PAGE 146 start reading .
 
if is was me I would condemn the lot.
 
what's the betting, he just put a pillow over his head or stood in the corner looking at the screen!
 
were in Blackpool is the job,so I can go on google earth?
 
with all is excitement ,I have just put the pop in the microwave .
 
  • Funny
Reactions: Zdb
I'm not installing. I'm reporting. And I'm reading from page 152 more importantly as it's static homes only. No caravans
the same, can be picked up and moved .with wheels under it or is it a boat !
 
From your pic and what you are saying it sounds an appalling installation and you need to be very conversant with the requirements to compile a concise and factual Report. Do you have GN8.
I do, been going through all night. And along with volt drop water ingress, max zs, corrosion and bad insulation, the main points I made in the post was the ones I was hoping people had the same thoughts or if different to share and elaborate
 
To my understanding because they are hard wired it all comes under sections 708 and 717 not 721?
they are not a house ,but a static caravan and can be up lifted not like house permeant.
I will give you a clue wheels on it .
 
They are type 4 Federal Electric devices and you need manufacturers data to compare Zs values. Sounds like you are out of your depth on this.
I’ve came across this type of DB before, and it had some newer mcbs fitted along the old ones, but they had to cut the lid of the DB to make them fit, unless they’ve put the wrong ones in and bodged it...

A3CA85F7-22DD-4F13-81F1-513579A3B30C.jpeg
 
717 or 721 are you not still in the same boat, or should I say caravan as the requirements regarding TN-C-S apply in both cases.
 
  • Like
Reactions: ruston
  • Creative
Reactions: ruston
upload_2018-1-20_16-19-8.png

made for the trailer trash ,got a tow bar ,has a house !
 
I have worked extensively in the static caravan park world. The only acceptable earthing arrangements for such buildings is TNS or TT.
TNCS can be used for supply upto external plastic meter box. Unit itself must be connected to earth rod and fed via 30mA RCD. I have also worked on units with SEB TNCS supplies housed in external meter cupboards. We never used the company earth and always fitted earth rods usually one was enough but quite often would fit 2 1 at each end of the concrete base and always tested the metal chassis and side walls to the earth connection.
 
  • Informative
Reactions: uksrevivor

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TNCS PME on caravan site with static caravan EICR
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32

Advert

Thread statistics

Created
fatgreeny09,
Last reply from
Sparkingmad,
Replies
32
Views
7,966

Advert