hi all i was just in the middle of doing an eicr on a caravan park and wanted some opinions on what codes are relevant to the site.

ive got tncs pme 100a 3 phase. each phase feeds a db like in the picture by a 100a main switch and 63 amp mcb and 10mm pyro (earthed with bonding clamp) which in turn feeds a static caravan by i think is 60898? 20a mcb (but could do with second opinion as im not as old as the mcbs) and 2.5 2 core swa connected directly to static home consumer unit again some earthed by bonding clamp at distribution board. no bonding at all to the chassis and no rcd except inside each static home

20180119_132736.jpg - https://drive.google.com/open?id=0BywXO5AAQnhsQkhwT002Q0NmdEpDUktXR01RVzhzZGxSVnZJ


all earth at the moment is exported from met tncs im thinking....


exported earth - c2
no rcd to each static home - c2
earth clamps on the swa c2 ( some are failing due to corrosion )
earth clamps on the pyro - c3
no extraneous bonding - c2
no earth at metal meters - c2

also these are not all defects just ones i was hoping for opinions on



ANNNDD... OPINIONS.... (plus abuse mildly welcomed !)
 
They are type 4 Federal Electric devices and you need manufacturers data to compare Zs values. Sounds like you are out of your depth on this.
I’ve came across this type of DB before, and it had some newer mcbs fitted along the old ones, but they had to cut the lid of the DB to make them fit, unless they’ve put the wrong ones in and bodged it...

A3CA85F7-22DD-4F13-81F1-513579A3B30C.jpeg
 
I have worked extensively in the static caravan park world. The only acceptable earthing arrangements for such buildings is TNS or TT.
TNCS can be used for supply upto external plastic meter box. Unit itself must be connected to earth rod and fed via 30mA RCD. I have also worked on units with SEB TNCS supplies housed in external meter cupboards. We never used the company earth and always fitted earth rods usually one was enough but quite often would fit 2 1 at each end of the concrete base and always tested the metal chassis and side walls to the earth connection.
 

Reply to TNCS PME on caravan site with static caravan EICR in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock