Morning All

I have a Hager TP+N Dis Board that i am installing later on this week. I need to purchase the switch disconnector for the board separately. Im unsure of which type to buy as i am getting conflicting statements.

Its Between:

4 pole 250A Switch Disconnector
3 pole 250A Switch Disconnector.

As its a TP+N board i thought the 4 pole would be better but one of the old boys say if their is a borrowed neutral it could become live!
 
Unless its TT then there isn't really going to be a requirement to install a 4pole incomer. Installing a 4 pole incomer could be a bad move if there were to be a UPS or similar referenced to neutral on the load side of the incomer.
 
Thanks for the help

Its a TNS earthing arrangement, 3 Phase with 400A per Line. This would be fed directly from the panel board on a 160A MCCB. When would you favour the 4 pole switch disconnector?
 
Hi - 537.2.1.1 says not necessary to switch the neutral if it is known to be reliably connected to earth via a suitable low impedance (as should be in your TN-S). In case others read this, for single phase domestic or similar then 537.1.4 applies and says we shall provide an isolation switch for both live conductors. Cheers, David.
 
Hi - 537.2.1.1 says not necessary to switch the neutral if it is known to be reliably connected to earth via a suitable low impedance (as should be in your TN-S). In case others read this, for single phase domestic or similar then 537.1.4 applies and says we shall provide an isolation switch for both live conductors. Cheers, David.

Cheers Wilko thats a good bit of info thier.
 
Hi - 537.2.1.1 says not necessary to switch the neutral if it is known to be reliably connected to earth via a suitable low impedance (as should be in your TN-S). In case others read this, for single phase domestic or similar then 537.1.4 applies and says we shall provide an isolation switch for both live conductors. Cheers, David.
I would keep the N closed too.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Tp+n Dis Board
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
LankyWill,
Last reply from
7029 dave,
Replies
9
Views
1,593

Advert

Back
Top