It is preferable that the supply to the garage isn't RCD protected, but that depends on whether the cable between the two is required by its type or installation method to be so protected. SWA doesn't need RCD protection, as long as the supply earthing isn't TT.
Hi Brian,

The cable is 6mm 2core and earth armoured swa. It will be earthed back to the main CU which is earthed to the incoming main as in the photo.
I have to mention though the I have installed a separate earth rod purely for off grid DC, solar panels, mttp charge controller and Battery which is in/on the garage. This rod is 20m away. Could that potentialy cause an issue?
 

Attachments

  • 20250421_141343.jpg
    20250421_141343.jpg
    883.2 KB · Views: 15
Joiner 🙂
His profile says “electrical enthusiast/ unqualified hobbyist” So, no, he’s not a pro. With a name like Chippy Minton, he’s either a joiner or lives in Camberwick Green :D

Just an observation. Not all sparks that are cps members are competent… in my opinion…
It’s like the cps give membership on however much the fee is, and the evidence of 1 job per year… which could cover dozens of workers.

Unintentionally altered. Once disconnected, it wouldn’t be hard to mistakenly put it in the wrong bar.

True. Maybe I should have said “report done on the house”

That photo looks like the incomer from the street.
It is the incoming main from the street
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Tripping issue with new installed 13 Way Dual Split Consumer Unit 2x100A RCDs (Type A) + 12 MCBs + SPD
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33

Thread Tags

Advert

Thread statistics

Created
Chippyminton0,
Last reply from
Chippyminton0,
Replies
33
Views
823

Advert

Back
Top