i have a TT system in a sorry state. please could you advise on these points
1.The earth cpc has snapped off the earth rod and is to short to reconnect Its is 2.5 csa. What is the required csa for the main earth 10mm or 16mm
2. there does not appear any bonding on the incoming gas supply. What is the csa required 6mm?
3. the consumer unit is rewireable type protected by a RCD (no sure if its 100ma) between consumer unit and incoming supply. 1 lighting circuit, 2 ring, 1 heating and electric cooker
what protection do i need in the new CU and should i remove the old RCD before the CU
thanks in advance
Mark
thanks in advance
Mark
hi mark,
looking at the questions you have asked i would employ the services of a local part p registered spark ;)
hi mark,
Thanks for the reply. I am fully quilfied but have not worked in the Industry for over 10 years. So as the old gray matter is a bit rusty just woundered if someone can refresh me as did not have much to do with TT in my practicing years. Also now is 17th edition
regards mark
Hi Mark,
A fair bit has changed over the years and its not something easily put across on a forum!
If you are thinking of getting back into it, it may pay you to sit the update course and get registered as this work would need notifying to your LABC.
A copy of the current 7671 along with the OSG would give you all the info needed.
However, a number of factors would dictate main earthing and bonding sizes which would need to be measured and calculated.
Normally 10mm main earth is fine along with 6mm for main bonding to gas and water, assuming no mechanical protection and test results permitting.
New CU should be dual RCD with not necessarily a stand alone RCD upfront as in days of old, providing your new CU is all insulated and of class II construction.
hi again mark,
what jason has said is spot on. things have changed a bit and this work would need either notifying through labc or you would need to employ a part p registered spark.
all the best ;)
thanks in advance
Mark
Hi mate you didnt state the incomming cable size. The Main Earthing can be worked out in 2 ways. Either by looking at Table 54.7 of the 17th edition or by using the Adiobatic. If your nos sure how to work the adiobatic use the tables is may be overkill but at least your covered.
The Gas ,Water,Structural steel has to have a main earth bond in place of at least 10mm Look at Table 54.8 for sizes.
As for changing the CU get someone whos part P qualified. I am in Scotland and not sure of part P so cant help you there. If your not fully qualified dont touch! The Rcds for the final circuits should be 30ma but if a new CU is getting fitted then it will be sorted then.
Hi Mark,
Thanks Jason
So just a standard split load CU with 30ma for socket protection would meet current regulations
regards Mark
Usee a small Merlin type 9 with 30ma Modular RCBOs on all circuits. 100A main isolator sorted (may be expensive:()
I bet it will be:D
Prices vary a fair bit, depending on make etc.
You are probably looking around £100+ fully loaded.
Pop into your local wholesalers.
They normally have specials on.:)
Speak to a wholesaler such as Newy& ayre, Edmonsons, City Electric, Electric centre and tell them what you need and they will get it for you. Dont accept the first price unless you are possitive its a good one
If your installation is in a sorry state, be aware that the lighting circuits, if they are up and down, woulld ideally be on seperate rcds This may become a problem with imbalance of the rcds if there is a shared neutral
Just a word of caution not to have to sudenly come up against this problem when changing consumer unit
6mm2 is the minimum size for the main protective equipotential bonding to the Gas service pipework on a TT system..although this only usully applies if the Main Earthing conductor is no more than 10mm2,,,,,,,on TNCs supplies the minimum bond is 10mm2
Lots of deals on CU's eg screwfix do a 10way split rcd wylex for £97.86 inc free x5 pendants & x10 dbl sockets.
Regards
Kung
Reply to TT Installation in need of some TLC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...