beaver74

in a t.t system i have all way thought you need a 100mA s type dp rcd covering the whole installation
been to a job today and it is a standard board dp isolator and filled with rcbo's which yes they will protect as for high earth loop but they are only single pole am i right in my thought's
 
My thoughts are that if every circuit is protected by a 30ma rcbo what is the need for a 100ma main rcd. I thought the 100mA rcd was to protect all "other" circuits when you could still have circuits on mcb only.
 
My thoughts are that if every circuit is protected by a 30ma rcbo what is the need for a 100ma main rcd. I thought the 100mA rcd was to protect all "other" circuits when you could still have circuits on mcb only.
yes but i am thinking that rcbos in general are single pole as apossed to double pole main rcd
 
in a t.t system i have all way thought you need a 100mA s type dp rcd covering the whole installation
been to a job today and it is a standard board dp isolator and filled with rcbo's which yes they will protect as for high earth loop but they are only single pole am i right in my thought's

This configuration of board is probably what the IET intended to be the norm with regard to 17th Ed compliance. Can`t see a problem with it myself.
 
Its a very expensive way of doing it tho! U can get DP RCBOs but they take up 2 modules; I used a 30ma to protect swa running a supply out to a garage.
 
I agree that a board full of rcbo`s is way too expensive for many jobs in the domestic sector - the dual rcd boards are far more viable. Cost aside, rcbo`s just take up too much room in the currently produced boards!
 
I was under the impression that rcbo's were all double pole.That is why you have to connect the neutral into them and why there is a curly blue
lead hanging out of them-all I have seen and used have also been one
module type.Incidently they can be bought for around 15 quid a pop.
 

Reply to tt system with rcbo's in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock