Got a job with a 60amp supplier head fuse. Contacted Eon re upgrading to 80amp or 100amp.
Their reply is they don't do that I need a qualified electrician!
 
Perhaps the planned load is higher than 60A. Shower and a cooker nowadays and you're about at 60A.
Yes. Shower cooker hot tub. Adding second shower wven with diversity I'm over budget. So requested a larger supply fuse.
I'll have to talk direct with Eon and clarify its their equipment not the customers. Maybe they think its the CCU breaker?
 
Yes. Shower cooker hot tub. Adding second shower wven with diversity I'm over budget. So requested a larger supply fuse.
I'll have to talk direct with Eon and clarify its their equipment not the customers. Maybe they think its the CCU breaker?

Ok sorted now. Just need to check tails are large enough.
 
DNO is sorted and booked but question is on tails now. They seem to measure around 10mm diameter (external) so I suspect 16mm CSA rather than the required 25mm CSA. DNO don't handle that so I may have to go back to EON to sort that.
What's the betting if I call to request bigger tails they refer me to a VET....
 
Am thinking if I have tails in hand he maybe tempted.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Ware Herts
Website
http://www.sparksofintelligence.co.uk
Business Name
Sparks of Intelligence

Thread Information

Title
Upgrading supplier fuse
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Pat H,
Last reply from
7029 dave,
Replies
15
Views
4,004

Advert

Back
Top