UK sparks are not trained to undertake fire risks and therefore checks abve ceilings should not be under our remit .......

Just saying
Because the cables run above and are easily accessible and electrical accessories and equipment are housed often above them then I’m afraid we would be negligent in not lifting up the ceiling tiles in my opinion.
If they were not accessible I’d agree :)
I agree on the fire risk point tho we often need to check that fire protection say between 2 floors in a riser housing electrical equipment such as the consumer units are fire sealed and fire compartments are not breached by cables passing through them.
They go on my report anyway.
 
I would not expect a suspended ceiling grid to have any real fire rating.
Whenever I install lights into a suspended ceiling, I try to keep the flexes off the grid by passing them over pipes, ducts, fan coil units etc.
 
Quite often you find the original cable tray above the suspended ceilings, all alterations and editions to the wiring are obvious because the altered cables are just flung across the ceiling not supported and even tie wrapped to air conditioning pipework.
Lovely job.
 
Quite often you find the original cable tray above the suspended ceilings, all alterations and editions to the wiring are obvious because the altered cables are just flung across the ceiling not supported and even tie wrapped to air conditioning pipework.
Lovely job.

Never a truer statement made

why do people think that chucking unsupported cables is a good idea?
 
With any luck a change to the regulations will bring home the message that it's unacceptable to simply fling cables over the ceiling grid, maybe even slow this 'race to the bottom' where uninitiated clients opt for the cheapest quote where the cowboys are planning to cut corners by not bothering with any containment.

It's actually already in the regs somewhere that you mustn't rely on other services to support your cables, partly because if the pipes or ceiling grid are taken down for an unrelated reason there'll be nothing supporting the cables at all and they'll just drape across the floor.

If the idea that you shouldn't do it because it's lazy and unprofessional isn't enough, maybe the idea that it's also dangerous will help.
 
With ceiling grids, the lights, smoke detectors, PIRs, etc. are installed after the ceiling is put up.
Even with step ladders, the height you can reach above the grid is restricted, so if the real ceiling is more than a meter above the false ceiling you are not going to be able to fix cables to anything other than existing services.
There is also the problem, that many lighting systems in false ceilings use Lighting Control Modules which the light fittings are plugged into.
The purpose being they can be unplugged to be replaced so tying the flexes onto containment is not an option.
Worrying about other services being removed is a bit pointless, as to remove them would entail first removing the ceiling grid and light fittings.
 
No cables are exposed as all are contained within trunking throughout the installation.
So you guys are saying I give it a C3 ? Im assuming that just applies to the escape routes (stairwells/corridoors etc) as per 521.11.201 and no coding for trunking across ceilings in all rooms.
Is this reg still valid?
 
In most circumstances I apply a C2 for this. There would need to be exceptional circumstances for me to conclude that it wasn't potentially dangerous and therefore only C3.
 
When we did the 18th @ college we sat in a classroom with a suspended ceiling,& asked the lecturer about the cabling above us supported by cable ties to the hangers.
He replied the ceiling is fire resistance for so many hours so no other fixings required....??
 
C2 by definition. It is potentially dangerous due to premature collapse in the event of a fire.
Why would it prematurely collapse, it has to be put up in accordance with the building regulations which require a ceiling to have a fire rating, all of this speculation is assuming that electricians has sufficient knowledge of the fire regulations to make an assessment of the danger, this is a specialist subject that any electrician should not get involved with IMO not part of the remit.
 
Make sure ceiling earthed nevermind thinking about fires..

I dont believe rules should be retrospective here and c3 should be appropriate. As when this stuff was installed it was signed off somewhere as fine.
 
Make sure ceiling earthed nevermind thinking about fires..

I dont believe rules should be retrospective here and c3 should be appropriate. As when this stuff was installed it was signed off somewhere as fine.

Are you saying the ceiling grid sections should be earthed?
 
Last edited:
I'm reading and says not todo it since 2005, I'm sure I've had todo it and seen it done few times... instructed todo it ...

But even if the grid metalwork did need earthing (or bonding), how could you ensure every strip is connected adequately. You would need earth links bolted between each separate piece, otherwise any contact is just fortuitous.

Crazy.
 

Reply to What EICR code for plastic trunking in escape routes? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock