Hi to all. I'm new and this is my first post.
I'm doing an EICR on a 3 story building split into multiple offices to let.
One thing I noticed is t+e cables in plastic trunking almost throughout (switch/socket drops, across ceilings to lights etc).
Would this be a code 2 or 3? Also would same code be throughout or just in escape routes?
I understand it could potentially be dangerous (causing entanglement when melting/falling etc), but surely an EICR is regarding electrical safety and as far as I can see the installation is electrically safe!
Any views as it would be a massive job to correct.
Surely if its a C2 then most commercial buildings in the country would fail?
Should I just C3 it and suggest landlord gets a fire safety report done?
 
UK sparks are not trained to undertake fire risks and therefore checks abve ceilings should not be under our remit .......

Just saying
Because the cables run above and are easily accessible and electrical accessories and equipment are housed often above them then I’m afraid we would be negligent in not lifting up the ceiling tiles in my opinion.
If they were not accessible I’d agree :)
I agree on the fire risk point tho we often need to check that fire protection say between 2 floors in a riser housing electrical equipment such as the consumer units are fire sealed and fire compartments are not breached by cables passing through them.
They go on my report anyway.
 
I would not expect a suspended ceiling grid to have any real fire rating.
Whenever I install lights into a suspended ceiling, I try to keep the flexes off the grid by passing them over pipes, ducts, fan coil units etc.
 
Quite often you find the original cable tray above the suspended ceilings, all alterations and editions to the wiring are obvious because the altered cables are just flung across the ceiling not supported and even tie wrapped to air conditioning pipework.
Lovely job.
 
Quite often you find the original cable tray above the suspended ceilings, all alterations and editions to the wiring are obvious because the altered cables are just flung across the ceiling not supported and even tie wrapped to air conditioning pipework.
Lovely job.

Never a truer statement made

why do people think that chucking unsupported cables is a good idea?
 
With any luck a change to the regulations will bring home the message that it's unacceptable to simply fling cables over the ceiling grid, maybe even slow this 'race to the bottom' where uninitiated clients opt for the cheapest quote where the cowboys are planning to cut corners by not bothering with any containment.

It's actually already in the regs somewhere that you mustn't rely on other services to support your cables, partly because if the pipes or ceiling grid are taken down for an unrelated reason there'll be nothing supporting the cables at all and they'll just drape across the floor.

If the idea that you shouldn't do it because it's lazy and unprofessional isn't enough, maybe the idea that it's also dangerous will help.
 
With ceiling grids, the lights, smoke detectors, PIRs, etc. are installed after the ceiling is put up.
Even with step ladders, the height you can reach above the grid is restricted, so if the real ceiling is more than a meter above the false ceiling you are not going to be able to fix cables to anything other than existing services.
There is also the problem, that many lighting systems in false ceilings use Lighting Control Modules which the light fittings are plugged into.
The purpose being they can be unplugged to be replaced so tying the flexes onto containment is not an option.
Worrying about other services being removed is a bit pointless, as to remove them would entail first removing the ceiling grid and light fittings.
 
In most circumstances I apply a C2 for this. There would need to be exceptional circumstances for me to conclude that it wasn't potentially dangerous and therefore only C3.
 
When we did the 18th @ college we sat in a classroom with a suspended ceiling,& asked the lecturer about the cabling above us supported by cable ties to the hangers.
He replied the ceiling is fire resistance for so many hours so no other fixings required....??
 
C2 by definition. It is potentially dangerous due to premature collapse in the event of a fire.
Why would it prematurely collapse, it has to be put up in accordance with the building regulations which require a ceiling to have a fire rating, all of this speculation is assuming that electricians has sufficient knowledge of the fire regulations to make an assessment of the danger, this is a specialist subject that any electrician should not get involved with IMO not part of the remit.
 
Make sure ceiling earthed nevermind thinking about fires..

I dont believe rules should be retrospective here and c3 should be appropriate. As when this stuff was installed it was signed off somewhere as fine.
 
Make sure ceiling earthed nevermind thinking about fires..

I dont believe rules should be retrospective here and c3 should be appropriate. As when this stuff was installed it was signed off somewhere as fine.

Are you saying the ceiling grid sections should be earthed?
 
Last edited:
I'm reading and says not todo it since 2005, I'm sure I've had todo it and seen it done few times... instructed todo it ...

But even if the grid metalwork did need earthing (or bonding), how could you ensure every strip is connected adequately. You would need earth links bolted between each separate piece, otherwise any contact is just fortuitous.

Crazy.
 
Why would it prematurely collapse, it has to be put up in accordance with the building regulations which require a ceiling to have a fire rating, all of this speculation is assuming that electricians has sufficient knowledge of the fire regulations to make an assessment of the danger, this is a specialist subject that any electrician should not get involved with IMO not part of the remit.
Remember collapse isn't how we see it; we see it as failing before the fire-rated time for the material (30-60-90 mins etc), in actuality the definition for 'premature collapse' on this instance is collapsing before firefighting activities (S&R, fire elimination, damping down) is completed and the crew removed, NOT the materials failing their rated times.

Love him or loathe him @widdler (SparkyNinja) did a webinar (and a 'history of') on the Regulation (521.11.201), with the help of his old man, from the POV of a firefighter and why it was so important to understand the broader intention of this Regulation.

Webinar;

History of:
 
Why would it prematurely collapse, it has to be put up in accordance with the building regulations which require a ceiling to have a fire rating, all of this speculation is assuming that electricians has sufficient knowledge of the fire regulations to make an assessment of the danger, this is a specialist subject that any electrician should not get involved with IMO not part of the remit.
If it’s in plastic trunking or conduit it may collapse. If it’s above plaster board it wont. so no code.
 
And, assuming it was needed, how would you ensure continuity to each piece of metal grid strip?
Cross bond each bit, durr.....obvious.

Get a roll of 4mm single cut into 6" strips with a ring crimp on either end, then an impact driver and a box of self drillers and Bob's your aunties brother.

Oh, nearly forgot the 16mm back to the MET. I usually run four of them just in case some clown alters the ceiling and removes one.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Pembrokeshire
Business Name
K H Electrical

Thread Information

Title
What EICR code for plastic trunking in escape routes?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
66
Unsolved
--

Advert

Thread statistics

Created
KevinH,
Last reply from
i=p/u,
Replies
66
Views
18,563

Advert

Back
Top