I think we have wandered far from the OP's questions!
So getting back to @Neptune then either a RCD or RCBO board would be a worthwhile improvement on your old rewirable fuse boards for lots of reasons, both the convenience of resetting and the additional protection offered by RCD, with the RCBO option slightly better in the event of any fault.
But the board is only one aspect of overall electrical safety:
www.toolstation.com
3-5 would be part of PAT testing in any rented property with landlord supplied appliances, but you can probably manage 3 & 4 yourself, and get a spark in to PAT test for 5 in any situation where you are not 100% sure the appliance (or extension lead) is good.
So getting back to @Neptune then either a RCD or RCBO board would be a worthwhile improvement on your old rewirable fuse boards for lots of reasons, both the convenience of resetting and the additional protection offered by RCD, with the RCBO option slightly better in the event of any fault.
But the board is only one aspect of overall electrical safety:
- Make sure all sockets are correctly wired and in good condition
- When you have RCDs, check at least twice a year they trip on the 'test' button.
- Inspect all of your electrical goods from time to time for signs of damage or stress to the cables, that the cables are properly clamped by the sheath in any plugs, and the plugs are not cracked/damaged or show overheating marks
- Check the appliances have the correct fuses fitted to any plugs
- Have appliances tested if in any doubt for soundness of earth and insulation