So I should code it as a C3 improvement recommended.
What is the improvement you recommend? How could you improve on a 60A switch being used for a fixed 52A load?
So I should code it as a C3 improvement recommended.
There a four 3kw storage heaters on this board. So a load of 52 amps been drawn.
So the load is under the 60 amp rating of the main switch.
I see your thinking now, so I won't code this.
Sometimes I need to stand back and look at what I'm seeing and thinking from a different angle.
Thank you for your advice.
Martin
There a four 3kw storage heaters on this board. So a load of 52 amps been drawn.
So the load is under the 60 amp rating of the main switch.
I see your thinking now, so I won't code this.
Sometimes I need to stand back and look at what I'm seeing and thinking from a different angle.
Thank you for your advice.
Martin
They'll most likely be 3.4Kw [or 2.55] so you're over 59 amps at 230volts if they're the larger heaters.
Well 230v is the declared single phase voltage throughout the country now even though nothing has really changed [apart from the network becoming ever more stretched to the limit] so that's what we have to base calculations on, I see what you're saying about the heaters though.
I have never seen the voltage at 230v, and am measuring everyday, the lowest I have seen it is 235v. Never seen 216v, but 250v yes. 315v but that was ug fault lol
Here I regularly measure bang on 230V.
That is not the declared voltage, it is the nominal voltage, something which some jobsworth in an office has written down and is impossible to implement. Nothing has changed because it cannot be changed, the whole country has substations with their output fixed at 250/433, there's nothing any jobsworth penpisher can do about that!
It doesn't change the basic physics though, If the stated power rating is at 240V you cannot just replace 240 with 230 in the calculation. The power dissipated will be less at 230V so the current which flows will be less.