Dec 4, 2011
71
18
83
Hi, I don't know if anyone can help with this. A customer called me out saying that a British Gas boiler service had highlighted a socket showing >2000 on the EFLI test. I went to look and got 1.12 on one side of the (two gang) socket and >2000 on the other. I assumed it was a dodgy socket and replaced it.
Testing the replacement I'm now getting about 1.15 as a loop test when the socket's off the wall but >2000 once I screw it in. I can't find any voltage on the back box.
Any ideas please?
Somehow earth continuity is breaking down. What do you mean by can't find voltage on the back box.
All I can think of is a dodgy connection on the different test lead or plug adaptor thingy. So you are getting decent-ish reading on the conductors, but a crap reading through a new socket, so have assumed you are using an additional test adaptor or a change of leads to do that test.
The initial fault sounds strange as it is difficult to disconnect the earthing from one side of socket but I suppose it is possible, it is more likely (but still unlikely) to have been a damaged earth connector at the socket, e.g. pushed to one side by the plug pin.
Once the socket front has been replaced I woudl assume that there is a poor connection to the earth terminal, perhaps the sleeving is caught on the screw, such that when the conductors are moved as the socket is screwed back the earth disconnects. This would be much more likely if both cpcs are in the same terminal or there is an earth discontinuity on one leg of the ring.
Sounds like the first socket must have been faulty. But the change as the socket is screwed in must be a break in the CPC (s) surely?
Maybe the cpc is nor continuous and the leg that does appear to be working has a break in it of which is aggravated when the outlet is pushed into place?
Are you using plug method and on L-PE? and as others said is it a ring circuit? And what was the gas man doing a loop test for ????
B.G did this with socket tester when they came to service our boiler asked why he said to prove boiler had earth (boiler on own circuit radial)
This whole thing dont make sense. If the boiler is on own radial then it has a spur yes? Where does the socket come into it? But anyway clearly the earth makes and breaks when the wires are in different position. And anyway a socket tester will not give you an ohmic measurement. Confused I am.
The socket tester that BG used was probably one of those that give a very rough idea of efli: there is one that has measurements something like <1; <5; >5 ohms. So when BG 'measure' it, there is no leeway for TT earthing.
To the OP, is the socket on a stud wall with a socket on the other side of the wall perhaps. The act of screwing back the face plate could be pushing the cable/conductors at an adjacent socket out of position.
Also test the R1 value with the face plate back, as it could be that and not the R2 causing the issue. Although I would suspect the CPC to be the cause.
Reactions: Vortigern
Is there a name for people who start threads and then decide not to respond to anyone's replies.
Reactions: Rpa07
Tis a bit rude to ask for advice and not reply. I had to cook the tea last night, but can still find a spare moment. :rolleyes:
Reactions: Leesparkykent
you cooked last night and still able to post today. i admire that.
Well, when I say cooked, I mean walked, yes walked to the chippie & got cod &chips twice.
And wots with all these boxes chippies use now, instead just rolling them up in paper?
Reactions: GMES
Corrected that for you mate.......Were have less of that northerner speak :D
Can't help it, the old man was from up North. Me Mom was from Barnet, so linguistically it's a frigging nightmare :fearscream:
Domestic socket loop test puzzle.
Domestic Electrician Forum
Bobble23,
The Ghost,