Think I've made a schoolboy error

Running a brand new 2kw electric fire from the mains via an extension.

Smelt burning tonight and found the plug and socket housing red hot after the fire switched itskit off.

Checked the extension plug to find it has only a 5 amp fuse inside.......

Is this the most likely reason the plug and socket got hot or is there something more sinister with the fairly new socket?

Cheers
 
The 5A fuse suggests the extension cable should not be running more than 5A, i.e. not the 8A of the fire.
 
Could be a combination of an undersized fuse, undersized extension cable, poorly terminated plug or poorly terminated socket.
 
The socket was fitted 4 weeks ago and has been alright, I'll take it off the wall tomorrow and check anyway, especially for the heat damage. The socket has cooled now though and inside the extension plug the brown wire has melted!
 
How about the pins of the plugtop? Melted plastic on the live pin?
Another photo?
Is that brown terminal tight?
Excited now!
 
It is hard to gauge the size of cable from your pic but the 5A fuse is underrated for a 2kw heater and theoretically it should have failed but it has not. It looks like a poor connection at the brown conductor and/or a combination of the fuse getting hot contributing to this. A 13A rated extension lead should resolve this but you should also get the socket it was plugged into checked out.
 
Although the live pin is tight,has it crimped the insulation instead of making a good connection to the copper? Is the fuse secure or does it turn easily?
 
Fuse is tight! Struggled to get it out to see the ampage! Hard to tell with the brown wire as it's melted, the fire had been blowing for a good four hours though before i smelt the dreaded burning plastic! Lol
 
Cheers everyone, I'll let you know what I find tomorrow out of interest.

I'll try plugging something else into the socket and see if it gets hot, or I'll buy a socket tester
 
Think I've made a schoolboy error

Running a brand new 2kw electric fire from the mains via an extension.

Smelt burning tonight and found the plug and socket housing red hot after the fire switched itskit off.

Checked the extension plug to find it has only a 5 amp fuse inside.......

Is this the most likely reason the plug and socket got hot or is there something more sinister with the fairly new socket?

Cheers
Was the extention lead coiled up?? Any loose conections any where??
 
When you say fire ? Are we talking full on flames ? Or just some smoke from melting plastic ? Good quality electrical fittings should be "fire retardant" !
 
looking at that, i'm going to design a coal fire that looks like it's electric. will be all the rage among the "keep up with the neighbours" brigade. this time next year i'll be a millionaire.

and it will revive the ailing construction industry as builders will be busy fitting chimneys to the silly new builds where the developer has forgotten to include them.
 
1ECE3DE4-4912-440E-BA75-05347EFC78D1.jpeg If you look at the attached curves, you will see that a 5A fuse will run at 8A for a considerable time before blowing, but the fuse will be getting very hot which is probably what caused the insulation to melt in the plug top.
People think that if you stick a fuse in it will blow as soon as it hits the rating of the fuse, this is simply not the case.
I went to a school a few years back, the DNO’s fuses were rated at 300A, but for most of the school day in excess of 400A was being drawn, fuses were failing about every 6 months due to fatigue and the cut-out was so hot you could not put your hand on it!
 
There wasn't even any smoke just a burning plastic smell!

It was a single plug extension at 5amp with no indication of ampage on the outside of the plug!

Any suggestions on a single extension? As there's no way the fire will reach the plug socket, it's about 2m off!

Everything you buy from B&M ends up rubbish!

The fire is this one

Adam Southwold Fireplace Suite in Oak with Colorado Electric Fire in Brass, 43 Inch | Fireplace World - https://www.fireplaceworld.co.uk/package/11500/adam-southwold-fireplace-suite-in-oak-with-colorado-electric-fire-in-brass-43-inch

Extension is this one wished I'd looked on website

Eveready 1 Socket Extension Lead 5m - https://www.bmstores.co.uk/products/eveready-1-socket-extension-lead-5m-299227

Socket is this

BG Twin Double Pole Switched Power Socket - 13A White | Wickes.co.uk - https://www.wickes.co.uk/BG-Twin-Double-Pole-Switched-Power-Socket---13A-White/p/148105
 
There wasn't even any smoke just a burning plastic smell!

It was a single plug extension at 5amp with no indication of ampage on the outside of the plug!

Any suggestions on a single extension? As there's no way the fire will reach the plug socket, it's about 2m off!

Everything you buy from B&M ends up rubbish!

The fire is this one

Adam Southwold Fireplace Suite in Oak with Colorado Electric Fire in Brass, 43 Inch | Fireplace World - https://www.fireplaceworld.co.uk/package/11500/adam-southwold-fireplace-suite-in-oak-with-colorado-electric-fire-in-brass-43-inch

Extension is this one wished I'd looked on website

Eveready 1 Socket Extension Lead 5m - https://www.bmstores.co.uk/products/eveready-1-socket-extension-lead-5m-299227

Socket is this

BG Twin Double Pole Switched Power Socket - 13A White | Wickes.co.uk - https://www.wickes.co.uk/BG-Twin-Double-Pole-Switched-Power-Socket---13A-White/p/148105
 
easiest way would be to get an electrician to add another socket or FCU close to the fire.
 
looking at that, i'm going to design a coal fire that looks like it's electric. will be all the rage among the "keep up with the neighbours" brigade. this time next year i'll be a millionaire.

and it will revive the ailing construction industry as builders will be busy fitting chimneys to the silly new builds where the developer has forgotten to include them.

Too late.

Dimplex have moved onto virtual reality
 
If you must use an extension lead then purchase one that is the right length presumably in your case about 3m and that is rated to 13A (there is rarely a reason to have an extension lead rated at less than this, to ensure problems do not occur).
The plug you have looks as if there has been arcing in the line terminal, the heat is localised to this area but has been intense but not spread.
 
Think I've made a schoolboy error

Running a brand new 2kw electric fire from the mains via an extension.

Smelt burning tonight and found the plug and socket housing red hot after the fire switched itskit off.

Checked the extension plug to find it has only a 5 amp fuse inside.......

Is this the most likely reason the plug and socket got hot or is there something more sinister with the fairly new socket?

Cheers
With this type of plug in which a screw is use to squash the conductor I would always use ferrules. My wife used an extension lead in which I had fitted with a 7 amp fuse so as not to cook the cable, it blow when she load it with a 2.2 kW shredder.
 
With this type of plug in which a screw is use to squash the conductor I would always use ferrules. My wife used an extension lead in which I had fitted with a 7 amp fuse so as not to cook the cable, it blow when she load it with a 2.2 kW shredder.
The fuse was doing it's job then.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Derby

Thread Information

Title
Schoolboy Error 2kw electric fire
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
36

Advert

Thread statistics

Created
Jamiec2018,
Last reply from
Pete999,
Replies
36
Views
13,195

Advert

Back
Top