Your immersion controller is a solarcache. They used to have technical guy called Trevor who was very helpful and maybe able to help you.
I have noticed that their website is down so I think you should try and get their contact details via midsummer
Hi - thanks for confirming that manual operation of the immersion heater does not make the A10 trip. Along the lines of #20 can you confirm it never trips with the immersion controller switched off? Perhaps it is seeing an overload when trying to balance sending power to the battery or the grid and immersion controller winding the load up and down in accord with its own programme (?). As you say, if immersion is left on 100%, the system does not trip.
Re: #9. Some more questions please.
1. Your diagram shows the Samsung A10 connected by a 'T' to the tails going to the consumer unit. Is this actually so? A picture would be helpful. I'd have expected the A10 to be connected to a circuit breaker in the consumer unit.
2. Where does the thin white wire shown on the left of the Absolute go to?
3. The current transformer are the devices which clip around the cables. Are they wired or wireless? Can you take some pictures?
4. Please confirm there is a current transformer clipped on the live or neutral leaving the A10. It must not be simply connected around both live and neutral. Again a picture would be helpful.
5. There should be another current transformer connected around one of the thick cables on the house side of the meter. A photo would be helpful.
6. Where is the A10 located? Is it getting too hot during the recent very warm weather?
Re the kettle : If I've understood correctly the immersion controller (when on auto) is continuously fiddling the current to the immersion and the A10 may trip. And when immersion is manually on or off the A10 behaves normally. I think the kettle on or off is same as immersion manually on or off. No continuous load adjustment and no A10 tripping, if that makes any sense. It's only a theory, with no data to support ...

From the picture all seems connected correctly. I have exhausted the things I would have checked, albeit - clutching at straws - I'd run a calibration sequence on the immersion controllers see section 5 of
https://midsummerwholesale.co.uk/pdfs/Solar-Cache-Installation-guide.pdf
I suspect the battery or the cooling system - two sub-systems of the A10 which age with operational use.
Here is a website which might help you find a technician to attend your home:
Samsung SDI ESS Energy Solar Battery | Solar Guide - https://www.solarguide.co.uk/solar-batteries/samsung-sdi-ess-energy#/
When you discover what was the problem it would be nice if you cold report back.
![]()