sterandall

hi, just looking for some help on how to install the main bonding on a large industrial building.
Firstly the supply neutral to the building is over 150mm so am i correct thinking i need to use 50mm bonding conductors for water etc?
Secondly the MET is about as fair away as possible on this site, there are MCCB boards all over the place with a 70+ earth to them and tray mounted earth bars with 50+mm earth to them, as long as i verify these are still connected can my bonding conductors come off of these?
I also need to install the bonding in another building on the same site for structural steel, water and hot water, the supply at this building is 25mm with a 70mm earth, what size bonding conductor do i need to use here? and can i just take it from the distribution board?

Any help and i will be very grateful, as ive never worked on a site this size and am pretty much lost in regards to what i can and cant do,

thanks
 
im unsure at the minute, il try and find out for tomorrow morning. I know theres 8 11kv transformers on site, dont know if that tells you anything?
 
Well, if the earthing is TN-S, then the bonding conductor need not exceed 25mm².
However if TN-C-S then 50mm² would be correct.
 
Thanks, what about the other seperate building on the site with the 25mm²?
Sorry forgot about that.
I don't understand why the earth is so much bigger than the supply, is it a typo?
If it is a typo, and the supply is 125mm², then both systems would require 35mm² bonding conductors.
If it isn't a typo, and the supply is only 25mm², then with TN-C-S, you would only require 10mm² for bonding.
If TN-S, you would have to verify the correct size earth is being used, one would normally expect the earth conductor to be only 16mm², with 10mm² bonding.
If the 70mm² earth is correct, you would need 35mm² bonding.
 
Last edited by a moderator:
If it’s an industrial site you can near guarantee it will be TN-S.
As to the 70mm earth I don’t know why. The company if first worked for 16 & 70mm was always on stock, anything else had to be ordered, could be a similar situation. It’s what they’d got so it got used.
 
Last edited by a moderator:
does anyone know if i can connect the bonding conductors to the tray mounted earth bars/MCCB board terminals? And if so would i need to trace the cables back to the MET and fit a 'safety electrical connection do not remove' tag at each connection? Everything ive read always say to take them to the MET but the actual METs are about as far away as possible on this site from all the stuff that needs bonding
 
I would connect a seperate earth bar to the earth terminal at the panelboards, and create an Earth marshalling terminal. This is very common on industrial sites ive worked on, and its the way that we bond the pumping stations and treatment works.
 
malc mentioned about steel frame earlier. He is hinting at the fact that it is permitted to use any extraneous metalwork as bonding or indeed CPC, provided precautuions are taken against its removal, and it is of a suitable CSA, which 90% of steelwork on a building will be.
 
Does this mean for say a ducting system i could take a bonding conductor from the structural steel to bond the ducting or did i misunderstand? sorry about all the questions but im pretty new to working in places like this and im quite interested in it.
 
yes you can. It must be labelled as usual, and of course the steel must be bonded to the main earth to the building. I would guess that it will be, but its worth checking.
 
yes you can. It must be labelled as usual, and of course the steel must be bonded to the main earth to the building. I would guess that it will be, but its worth checking.

i never knew that, that makes life a hell of a lot easier now though thanks, the structural steel is bonded in about 240mm. When you say precautions must be taken against its removal is that just as simple as labeling it?
 
the bonding connnection should be labelled with a label not less than that of a BS951 clamp. other precautions are things like not connecting to steel that is likely to be removedand maybe enusring that removal of any cable in the building by non sparks requires the permission of the electrical engineer.
 
If the building is all structural steel and has been bonded back to the MET at origin, you can safely say that the whole of the steelwork is one big bonding conductor that is interconnected by cross beams and sections etc!! haha!! Just try isolating all those parallel earth paths, ...no chance!! The chances are, that the structural steel of these buildings is also forming part, if not all of the earthing for the site too.

As you say, ...you can just link the steelwork to the system or service you want to bond out. In reality, the chances are it's already bonded by fixings etc,, but you will still need to make purpose made bond connections, to satisfy all the various requirements you have these day's...

Be interesting to know what sort of Ze and/or Zs values you get at the buildings incoming supply point??
 
When bonding the steel work use clamps for the connection or weld a bolt on, don’t drill structural steel. If you weld a bolt then put it inside the web out of harms way.
 
I'll be using clamps on the structural steel, had a quick scan through the catalogue last night and found them.

Thanks everyone for all the help
 
malc mentioned about steel frame earlier. He is hinting at the fact that it is permitted to use any extraneous metalwork as bonding or indeed CPC, provided precautuions are taken against its removal, and it is of a suitable CSA, which 90% of steelwork on a building will be.

Thanks John yes that was what I was going to post next that the actual building frame will be the bonding conductor, but was not on the forum for the last few days, but you E54 and Tony sorted the lad out.
 
When bonding the steel work use clamps for the connection or weld a bolt on, don’t drill structural steel. If you weld a bolt then put it inside the web out of harms way.

hi whats the issue with drilling the structural steel work ?? we drill and tap the hole, clean the area where the crimp is to go from paint and install the bond accordingly ! just wondering if there was something wrong with this ??
 
In the real world, the chances are, there would be Nothing wrong in drilling and taping in substantial sections of structural steel work. We have to get approval on our projects for all such work from the Structural Engineer, but i can't ever remember being refused, ...even once!! Braised, spot, or exothermically welded studs are also useful for connecting bonding/earthing cables to steelwork

Different if you need to chop a lump out of a section of structural steelwork, but that would be an extremely rare occurance...
 
hi engineer, thanks for the info. i kinda thoght thats what netblindpaul was on about, i have never had this method questioned ! the plant were on is a large job and the enginners and fitters drill holes all over the place for securing plant and walkways etc and its never broughgt up any issues so i cant see how a M8 or M10 hole that has a bolt in it woulld make a hell of a difference pepole secure various items on the structural steal work on many sites and again never heard any one including site agents or the enginners bring the subject up , i am sure i would hear about it !
 
hi engineer, thanks for the info. i kinda thoght thats what netblindpaul was on about, i have never had this method questioned ! the plant were on is a large job and the enginners and fitters drill holes all over the place for securing plant and walkways etc and its never broughgt up any issues so i cant see how a M8 or M10 hole that has a bolt in it woulld make a hell of a difference pepole secure various items on the structural steal work on many sites and again never heard any one including site agents or the enginners bring the subject up , i am sure i would hear about it !

As you have said , steel erectors/structural engineers etc drill in to these beams to bolt in cross strainers so tapping/or bolting, an earth wire would be hardly putting any stress on the beem the removed swarf when drilling would be replaced with a bolt so the volume of the beam would be the same( the bolt would infact would be of stronger composite) so there for would not be any weaker

Also as you say roller doors etc are all fitted to structural steel work ,maybe we better do away with them and fire doors .
 
The nature of the steelwork makes the difference. Most of the plants I’ve worked on the steel structure formed part of crane support tracks. I wouldn’t contemplate drilling a stanchion or beam that had anything to do with the integrity of that structure. Cross bracing still needs to regarded with care.

I’ve seen 1½“ bolts popped out of joints. In one fish plate joint 24 out of 72 bolts had failed!

A wild supposition it may be but in court anything that can be used to disperse/spread blame, will be.

Cover yourself!
 
Seriously ?? we are talking about a wee hole in a H beam here, i am going to ask the structural steel enginner on the job next time i see him ?
 
As you have said , steel erectors/structural engineers etc drill in to these beams to bolt in cross strainers so tapping/or bolting, an earth wire would be hardly putting any stress on the beem the removed swarf when drilling would be replaced with a bolt so the volume of the beam would be the same( the bolt would infact would be of stronger composite) so there for would not be any weaker

Also as you say roller doors etc are all fitted to structural steel work ,maybe we better do away with them and fire doors .


You have to take these things in perspective, just because you see a contractors steel erectors fixing, hangers, and making other alterations that is involving drilling and bolting to existing structural steelwork, doesn't mean they are doing this without clearance from a structural Engineer. Remember in most instances they would need to submit drawings for approval, before any work would commence either from the companies Engineering dept, or via a LABC or whatever.
Another possibility is that the contractor is following a drawing issued by a companies Engineering department or by the companies consulting engineer.

In general, the drilling and tapping a single hole for say a 14 to 17mm earth bonding cable is neither going to be here nor there in the bigger scheme of things...lol!!
 
Generally it should not be a problem, however if as Tony suggests the steelwork is load bearing as in for a travelling gantry crane say and thus is subject to stress cycles, then drilling even a 5mm hole could be an issue, especially if the steel work has been value engineered, or the crane loading has been upped to its maximum, perhaps above the original design, but within the loading of the steel work as is.
You then come along and insert a crack nucleation point (several actually if you tap the hole) in a cyclically loaded structural member.
This could be an issue...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Main bonding in large industrial building
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
35

Advert

Thread statistics

Created
sterandall,
Last reply from
netblindpaul,
Replies
35
Views
9,512

Advert

Back
Top