Guest viewing is limited
i had to use more than 6 letters!
- - - Updated - - -
and i'm new so need 6 post or more before i can use my profile, i hope these count....
Not necessarily.
BS7671:2008 Amdt 2011, 514.13.1 (iii): "A durable label .... shall be fixed ... at ... the main earth terminal, where separate from main switchgear."
So, if it's adjacent to the main board, head, meter, etc, I would say no. After all, how many PME earth terminals do you see with a label?
i would say yes as the MET is separate from the main switchgear which is inside the CU.
Yep has to have one I use the yellow and black stickers, but you could just use the metal label off a BS951 earth clamp
Tel is spot on as usual
safety electrical connection do not remove notice
seftonbarn,
grantr37,