If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
I'm a trainee and about to start doing jobs for my portfolio which includes replacing a CU and I'm wondering if it is still acceptable to install consumer units onto non-combustible material or was it ever acceptable? The relevant regulations appear to be:

131.3.2 Persons, livestock, fixed equipment and fixed materials adjacent to electrical equipment shall be protected against harmful effects of heat or thermal radiation emitted by electrical equipment, and in particular the following: (i) (ii) (iii) Combustion, ignition, or degradation of materials Risk of burns Impairment of the safe function of installed equipment. Electrical equipment shall not present a fire hazard to adjacent materials

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall: (i) have their enclosure manufactured from non-combustible material, or be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12. NOTE: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.

527.1 .2 A wiring system shall be installed so that the general building structural performance and fire safety are not reduced

421.1.201 and 527.1 .2 are quite specific in that they refer to consumer units/switchgear/wiring however 131.3.2 refers to "fixed materials adjacent to" as I've highlighted in bold so would it be fair to interpret that as meaning the material we mount a cu onto ?
 
Last edited by a moderator:
  • Like
Reactions: old_guy
'm wondering if it is still acceptable to install consumer units onto non-combustible material or was it ever acceptable?
Do you mean combustible, not non-combustible?

131.3.2 Persons, livestock, fixed equipment and fixed materials adjacent to electrical equipment shall be protected against harmful effects of heat or thermal radiation emitted by electrical equipment, and in particular the following: (i) (ii) (iii) Combustion, ignition, or degradation of materials Risk of bums Impairment of the safe function of installed equipment. Electrical equipment shall not present a fire hazard to adjacent materials
I think this means under non-fault conditions. A CU wouldn't get so hot in normal use to set fire to a timber board that it was mounted on, for example. Interested to hear other members opinions.

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall: (i) have their enclosure manufactured from non-combustible material, or be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12. NOTE: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.
527.1 .2 A wiring system shall be installed so that the general building structural performance and fire safety are not reduced
This means, for example, not compromising the integrity of a fire compartment by fitting non-fire-rated downlights. That sort of thing.
 
Do you mean combustible, not non-combustible?


I think this means under non-fault conditions. A CU wouldn't get so hot in normal use to set fire to a timber board that it was mounted on, for example. Interested to hear other members opinions.



This means, for example, not compromising the integrity of a fire compartment by fitting non-fire-rated downlights. That sort of thing.
Thanks. Yes, I meant combustible.
 
Is says if you are putting a metel consumer unit in. So I affect it's metel
Fire rated.
Thanks but I
Is says if you are putting a metel consumer unit in. So I affect it's metel
Fire rated.
Understood and I get that its common practise to use ply. Being inexperienced as I most definitely am, just wondering why we dont use cement backerboard considering that 131.3.2 does appear to leave things open for debate.
 
If staring from scartch, then use fire board, if existing use the what is their..
1741958035652.jpeg
 
  • Like
Reactions: old_guy

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
cu mounting materials
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
old_guy,
Last reply from
old_guy,
Replies
6
Views
270

Advert