Are we talking about CHris the handyman youtuber sparky plumber builder Tiler plasterer gezza man

 
Last edited by a moderator:
Cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than: · 1.0 mm for the horizontal top surface and · 2.5 mm for all other surfaces of the enclosure that are accessible after installation. For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above. Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.
 
Cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than: · 1.0 mm for the horizontal top surface and · 2.5 mm for all other surfaces of the enclosure that are accessible after installation. For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above. Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.
well done Charlie I could not put it better me self .
 
It really is out of control they will want us to make it fully air tight and pressure test it before were done
I was told initially sometime back that the consumer units need not be sealed because the main accelerant was the plastic CU so the steel CU was enough to stop a spread of fire, my question at the time was if the plastic CU were to be replaced with steel what about the MCB and plastic blanks why are they not being replaced with a fire proof alternative.

The answers I've been told is, the fires start from loose terminals in the tops of MCB's and the flames melt the plastic CU which spreads the fire, so any opening below the top of the CU doesn't need sealed, hence the reason why I bring my cables in through the back knock outs and I only put flexible grommet strip round to stop damage to the outer sheathing.

An alternative I was told about was to install a length of deep trunking along the top of the CU and run all cables into the trunking through the knockout in the top of the CU but I'm skeptical that that would work.

I personally don't like the look of loads of glands poking out the top of a CU I prefer them to come out the back.


OPINIONS OPINIONS OPINIONS!!!!
 
I was told initially sometime back that the consumer units need not be sealed because the main accelerant was the plastic CU so the steel CU was enough to stop a spread of fire, my question at the time was if the plastic CU were to be replaced with steel what about the MCB and plastic blanks why are they not being replaced with a fire proof alternative.

The answers I've been told is, the fires start from loose terminals in the tops of MCB's and the flames melt the plastic CU which spreads the fire, so any opening below the top of the CU doesn't need sealed, hence the reason why I bring my cables in through the back knock outs and I only put flexible grommet strip round to stop damage to the outer sheathing.

An alternative I was told about was to install a length of deep trunking along the top of the CU and run all cables into the trunking through the knockout in the top of the CU but I'm skeptical that that would work.

I personally don't like the look of loads of glands poking out the top of a CU I prefer them to come out the back.


OPINIONS OPINIONS OPINIONS!!!!
I would love to meet the people that make these rules. Admittedly I like the metal boards a lot more than the plastic ones as they had a real cheap feel to them but it's getting over the top. Have to be careful with the rest entry through wood because wood burns can't win going to have to carry a sheet of fire board with me now as well as all the other rubbish
 