If You are going to mount the CU on wood then just paint the wood in a fire retardant paint first.


I paint it in something like this, you can get it cheaper than quoted on the link.
I bought a tin a while back and coated a few sheets of ply, I then just cut out what I need for the CU then touch in the cut edges with the paint.
Its probably a bit over kill, but for a few extra quid it gives me peace of mind. I print off the data sheet to the paint and put it in with the EICR.

Why bother, the new CU being metal, means it won't catch fire :)
 
  • Like
Reactions: leebut
  • Like
Reactions: Andy78
Yeah......but with the class of some of todays terminations...:(…….and some working on 'em...:(:(
Sometime people are over tightening the terminals and they’re damaging the cable connection hence why they want us to us Torque screwdrivers
Why don’t manufacturers just make a ‘19th addition’ non combustion bomb and fire proof surface mounting accessory for domesticated consumer unit wiring.

Kind like a surface wiring patters just much larger and supply with it a tube of flame retardant sealant to caulk in any gaps or holes
why do we just line the CU with asbestos!!
 
Sometime people are over tightening the terminals and they’re damaging the cable connection hence why they want us to us Torque screwdrivers

why do we just line the CU with asbestos!!

Near every site sparks I watch doing a consumer unit , uses an impact driver anyway (and no I’m not joking) annoyingly I can’t find the video but there was a new build sparks on you tube who installed a brand new 17th Ed consumer unit using nothing but an impact driver.

Box it in using asbestos would probably achieve a better fire rating ?
 
Last edited by a moderator:
  • Like
Reactions: leebut
To be fair you can only act on the information you have and from the little bit of the video I watched it sounds like he got duff information on his course.
 
  • Like
Reactions: FatAlan and Andy78
To be fair you can only act on the information you have and from the little bit of the video I watched it sounds like he got duff information on his course.
Totally agree. He comes across as one that listens to whatever is said to them then spits it back out without thought. It's a common trait in our industry these days. So much misinformation about. I really think the IET needs to be more proactive with publicly clarifying information related to regulation changes. This could only benefit the industry.
 
  • Like
Reactions: ferg
I’m glad my videos bring awareness to such grey areas in the industry. This is exactly why I make videos on a public format so they get shared around and discussed. Appreciate any feedback good or bad. Even though some of you guys are damn right nasty without even knowing me.
 
Hi Chris

I am a fan of you videoblogs

I think you do a good job of explaining what you are doing and why you are doing it

Keep up the vids mate
 
  • Like
Reactions: Toneyz
@Reevio , where did you get your guidance re sealing cable entries with intumescent sealer?
 
Maintaining the fire integrity of a metal consumer unit surely is common sense no?
My jtl guy that did our 18th is also an NICEIC inspector he was very passionate about fire safety to the point we should also be fitting intumescent pads in the back of plastic boxes in stud partitions. A little added protection never hurts anyone and for the sake of £2.89 I will continue to do so.
 
  • Like
Reactions: Toneyz
Did this genius of an inspector tell you where in the Regulations that additional fire protection must be put in place. The Regulations state they should be constructed from non-combustible materials. It should be remembered a consumer unit enclosure is not a fire barrier but just a non-combustible enclosure. To manufacture a consumer unit which acts as a fire barrier would not be practical or cost effective.
 
As has been mentioned before the CU's are now manufactured from non-combustible material therefore there's nothing to combust therefore fire-sealing is not required.
 
As has been mentioned before the CU's are now manufactured from non-combustible material therefore there's nothing to combust therefore fire-sealing is not required.

What about all the items within the CU that can combust?
 
  • Like
Reactions: MFS Electrical
I can see merit in sealing any large gaps or holes in the top or sides of the board ,
1 to maintain the correct IP rating
2 to improve any lost fire integrity

But I personally think all this fuss about avoiding plastic boxes , plastic clips , plastic wall plugs and plastic glands is ridiculous.
 
Last edited by a moderator:
Maintaining the fire integrity of a metal consumer unit surely is common sense no?
My jtl guy that did our 18th is also an NICEIC inspector he was very passionate about fire safety to the point we should also be fitting intumescent pads in the back of plastic boxes in stud partitions. A little added protection never hurts anyone and for the sake of £2.89 I will continue to do so.
Hi Chris


Where will this end it’s not a building regulation or more a wiring regulation to fit intumescent pads in drywall boxes, it’s just someone’s take on the regs not actually the regs.

If it was a regulation for fire integrity the edges of the CU would have intumescent seals also the hinged lid would too, most manufacturers have top hinges to stop the spread of fire but the odd manufacturer has bottom hinge with a magnetic catch fire could spread from the front but like I say it’s NOT a regulation to seal it.

Makes no sense to seal everything it makes the job harder for the next man to come along when he’s adding the extension etc

Lee
 
Why bother, the new CU being metal, means it won't catch fire :)

Because I've have OCD's :D

I also worked on a building where a metal control board set on fire inside and the heat was intense enough for the wooden partition next to it to spontaneously com-busted, even though the flames did not escape the metal enclosure. I was quite astonished by this at the time and it stuck in my mind.
 
Because I've have OCD's :D

I also worked on a building where a metal control board set on fire inside and the heat was intense enough for the wooden partition next to it to spontaneously com-busted, even though the flames did not escape the metal enclosure. I was quite astonished by this at the time and it stuck in my mind.
 
So in effect, you form a chimney in a plastic flammable material, (I'm assuming plastic as I've never seen sticky back metal trunking), with an opening from the CU into the chimney? Bit like cladding a tower block??
I use the sticky trunking to stand my metal clad consumer unit off the wall or wooden back board so my cables all enter the board through the rear entry holes so that flames from this non existent fire can’t escape the CU, I very rarely knock a knock out of either the sides or top
 
I use the sticky trunking to stand my metal clad consumer unit off the wall or wooden back board so my cables all enter the board through the rear entry holes so that flames from this non existent fire can’t escape the CU, I very rarely knock a knock out of either the sides or top

One thing I like about Hager & Wylex CU's, is they also manufacturer (metal) wall spacers for their products. Not cheap, but look better than anything I could replicate.
 
  • Like
Reactions: richy3333
Maintaining the fire integrity of a metal consumer unit surely is common sense no?
My jtl guy that did our 18th is also an NICEIC inspector he was very passionate about fire safety to the point we should also be fitting intumescent pads in the back of plastic boxes in stud partitions. A little added protection never hurts anyone and for the sake of £2.89 I will continue to do so.

I've posted this vid a few times now, and it is getting a bit old, so the guidance isn't current, but I can't see things have changed that much. 3.55mins discusses CU's & sealing thereof;

https://electrical.----------/wirin...l-discussion-1-at-the-elex-show-in-harrogate/

I think using sealant of any kind, is a bit of a bodge. A CU by nature will need additions from time to time; its not like sealing a bath, shower etc.
 
Because I've have OCD's :D

I also worked on a building where a metal control board set on fire inside and the heat was intense enough for the wooden partition next to it to spontaneously com-busted, even though the flames did not escape the metal enclosure. I was quite astonished by this at the time and it stuck in my mind.

A larger distribution board in a commercial or industrial setting, might need different considerations; a simple domestic CU does not need all these fire retardant measures.
 
Last couple of CU's I've done, where the cables come through large rear entry I've sandwiched a piece of intumescent pad between the enclosure and wall/board prior to fixing the enclosure. Ive then cut a cross in the pad, fed the cables through and then moulded the pad back round the cables as they enter to reduce and seal the gap. Not sure if thats better than filling with sealer or worth the effort especially if its a busy box.
 
bad enough having to seal cut-out fuses and meters without all this crap as well.
 
  • Like
Reactions: ipf
Last couple of CU's I've done, where the cables come through large rear entry I've sandwiched a piece of intumescent pad between the enclosure and wall/board prior to fixing the enclosure. Ive then cut a cross in the pad, fed the cables through and then moulded the pad back round the cables as they enter to reduce and seal the gap. Not sure if thats better than filling with sealer or worth the effort especially if its a busy box.

Why for so? If the cables came out of a cavity (naughty) perhaps. Just out from the back, I don't see why you should go to that expense.

I'm no longer current, but have you ask your scheme for guidance?

All this extra work cost someone money, and it seems to me to be an unnecessary.
 
One of the installs was on a board mounted on couple of patterns to allow access from behind. Goes back to previous threads about mounting on wood which numerous meters and CU's seem to have been mounted on over the years.

Must admit the lower specified IP ratings for the side and bottom of enclosures doesn't exactly support a case for making the enclosures sealed enough to prevent a chimney effect as I believe someone mentioned earlier.

If we were serious about reducing the risk of fire due to poor or loose connections perhaps the manufacturers should come up with a design that eliminates having to get a small bit of exposed copper into a barely visible slot and then tighten up a screw!

Some of the kit we are asked to install is utter c**p when it comes to any consideration that has been given in respect of ease or practicality of installation.
 
I’m glad my videos bring awareness to such grey areas in the industry. This is exactly why I make videos on a public format so they get shared around and discussed. Appreciate any feedback good or bad. Even though some of you guys are damn right nasty without even knowing me.
@Reevio - It's somewhat childish to refer to us on this forum as a bunch of old women. You to are a member and therefore by definition must be an old woman also? :)

Here is my feedback, 'good or bad'...

The thing with Youtube is to a certain extent watchers do know you in thatchy know the quality of the work you do and whether it is right or wrong.

I've seen a few of your videos and do applaud you that you have the aptitude to do the videos. You clearly have your sycophants by virtue of some of the comments they make. I watched the videos for entertainment value not for technical content or quality. I've seen you give totally wrong statements/advice in your Youtube comments and again totally wrong information in the videos.

An example that springs to mind is the house where the owner took down a stud wall in the kitchen/lounge area. You jointed the cables using Wago connectors and then ----ed the lot in the ceiling void utilising either a Wagobox or a Wagobox light professing it was mainatenece free. It clearly was no such thing in the manner you had installed it and you could not have ever looked at any Wago literature on how to install the things.

I've also seen you install downlighters way too close to timber joists thinking that is ok to do.

I regret to say that I have a first year apprentice that knows both of the above examples are a not correct.

Can I ask your background because sometimes you are CRS, sometimes HRS. Most of your videos are electrical based but there were some where you did building work. Are you a builder by trade? Did you do an apprenticeship or a Electrical Trainee course?

I don't think the situation surrounding fire sealing is a grey area and other more respected and knowledgeable people on here have already pointed out your errors.

I dont think you make these videos to 'highlight grey areas and so they get shared around and discussed' (my paraphrasing) because if that were the case you'd not be making 'bog standard videos' of domestic rewires et al. How do they shed light on grey areas of the industry? You're a member here. I challenge you to post your 'grey area' videos here first for industry discussion, though I anticipate you won't have the nerve to do so???
 
Why don’t manufacturers just make a ‘19th addition’ non combustion bomb and fire proof surface mounting accessory for domesticated consumer unit wiring.

Kind like a surface wiring patters just much larger and supply with it a tube of flame retardant sealant to caulk in any gaps or holes
Because they need to sell us Amd. 1,2 & 3 regs books etc first.
 
  • Like
Reactions: Strima
I cannot believe the lengths people are going to to fire proof a non fire proof enclosure.
 
@Reevio - It's somewhat childish to refer to us on this forum as a bunch of old women. You to are a member and therefore by definition must be an old woman also? :)

Here is my feedback, 'good or bad'...

The thing with Youtube is to a certain extent watchers do know you in thatchy know the quality of the work you do and whether it is right or wrong.

I've seen a few of your videos and do applaud you that you have the aptitude to do the videos. You clearly have your sycophants by virtue of some of the comments they make. I watched the videos for entertainment value not for technical content or quality. I've seen you give totally wrong statements/advice in your Youtube comments and again totally wrong information in the videos.

An example that springs to mind is the house where the owner took down a stud wall in the kitchen/lounge area. You jointed the cables using Wago connectors and then ****ed the lot in the ceiling void utilising either a Wagobox or a Wagobox light professing it was mainatenece free. It clearly was no such thing in the manner you had installed it and you could not have ever looked at any Wago literature on how to install the things.

I've also seen you install downlighters way too close to timber joists thinking that is ok to do.

I regret to say that I have a first year apprentice that knows both of the above examples are a not correct.

Can I ask your background because sometimes you are CRS, sometimes HRS. Most of your videos are electrical based but there were some where you did building work. Are you a builder by trade? Did you do an apprenticeship or a Electrical Trainee course?

I don't think the situation surrounding fire sealing is a grey area and other more respected and knowledgeable people on here have already pointed out your errors.

I dont think you make these videos to 'highlight grey areas and so they get shared around and discussed' (my paraphrasing) because if that were the case you'd not be making 'bog standard videos' of domestic rewires et al. How do they shed light on grey areas of the industry? You're a member here. I challenge you to post your 'grey area' videos here first for industry discussion, though I anticipate you won't have the nerve to do so???
Give me a call tomorrow we can have a chat
 
I can't believe that there are still queries about 18th edition this far on after it was introduced.
 
I can't believe that there are still queries about 18th edition this far on after it was introduced.
We still get queries about the 14th edition ….
 
  • Like
Reactions: Reevio
All this fuss over pretty much nothing...

If you want to caulk your fuse board then knock yourself out

If you don’t want to caulk it then fine just leave it caulk free
 
  • Like
Reactions: Reevio
spot-on best comment in this thread so far .

I'd be pretty Pee'd off if I went to a job to add a circuit and someone had filled the rear entry with sealant for absolutely no reason.

By publishing your point of view as best practice or regulation you are encouraging others to think the same way. Inexperienced sparks and potential customers.

Spreading misinformation by accident is one thing but continuing to do it once you know better is something else.
 
  • Like
  • Agree
Reactions: mainline and DPG
I'd be pretty Pee'd off if I went to a job to add a circuit and someone had filled the rear entry with sealant for absolutely no reason.

By publishing your point of view as best practice or regulation you are encouraging others to think the same way. Inexperienced sparks and potential customers.

Spreading misinformation by accident is one thing but continuing to do it once you know better is something else.
Please don’t exaggerate. Let’s be honest all I’m doing is filling the gap next to the cables that didn’t get filled.
You’d be a better man than me if you could add an extra circuit in a consumer unit mounted to the wall. Without 1 having to cut a patch in the ceiling or wall. 2 having to remove the consumer unit to gain entry.
Let’s be honest there are 2 other available knockouts on the rear of the consumer unit and around 10-12 available knockouts on the top? Appreciate your comment.
 
I use the sticky trunking to stand my metal clad consumer unit off the wall or wooden back board so my cables all enter the board through the rear entry holes so that flames from this non existent fire can’t escape the CU, I very rarely knock a knock out of either the sides or top
The fact you have created a void behind the CU with access for any heat and gases through the rear entry and into the void is, in effect, a chimney, with the possibility of, if gets hot enough, melting or setting fire to the top bit of trunking and therefore improving the chimney effect.

As others have said, I think there is a tendency, because of all the urban myths, to over think what should be a simple install. Just fix it to the wall, or a board, or whatever, that's what it was designed for without any revenue generating add ons from various manufacturers.

It's not supposed to be fire proof. It's designed to contain a fire within if one should occur. If a fire should occur there is not much in there that's going to burn anyway, which was the point in getting rid of the plastic.

Don't over think it and risk making it worst.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bury

Thread Information

Title
Sealing a consumer unit entry points??
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
128

Advert

Thread statistics

Created
leebut,
Last reply from
Simon47,
Replies
128
Views
61,638

Advert