Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer unit was extended at some point:

20230623_111449.jpg


The additional unit is from the kitchen as they had a new kitchen fitted. My concerns are with the quality of the work. No glands are used and all wiring enters the side, the cables also have sheathing cut short so the wires are exposed. I'd have thought some simple chaffing could expose a wire and short the consumer unit:


20230623_111454.jpg


Due to these concerns I opened up the box to take a look at the method used to extend the wires:

20230623_111557.jpg


I have a few questions here... why are glands not used? Is it ok not to use a DIN rail and simply extend all circuits with lever terminals? If so, would splice connectors 221-2411 not be more suitable? If the cables aren't long enough to reach a DIN rail, would it be best to use a Wiska Consumer Unit Relocator for any circuits that do have a wire long enough, and then extend the others?

I'm assuming this is legal, but sloppy work.
 
It's rough but, provided connectors are able to handle the rated current of each outgoing circuit, there's no real issue on that front.

Cables should indeed be restrained and IP rating of enclosures maintained. The main issue, as you've highlighted, is cable sheaths and exposed insulation entering through a cut metal edge. There are a number of ways this could be resolved and glanding individual cables is one of them. To make the best of what you have, I'd probably replace the 2 gang surface box with a small adaptable box and run a short length of 2x2" PVC trunking between it and the board, which would provide space to place some sort of gromment over that cable entry.

I'd be slightly concerned about what's inside your CU, but it may all be fine.
 
Those Wagos are poorly connected, far too much insulation stripped from them. The bottom one appears to have two cpcs in the same sleeve into one terminal. It doesn't bode well for what the consumer unit contains.
 
Cut that box the get the cables out without dissing the wagos. Replace with a Wago XL box, which has cable restraint built in. Then tidy up the connections 1 at a time. Be nice to see a pic. of the CU wiring.
 
Cheers all, I like the idea of a Wago XL box - I'll have to check if the original cables are long enough to reach a box as they seem to be quite short.

Here's the CU:

20230624_083432.jpg

20230624_083619.jpg



Seems ok although not the neatest and the grommet looks cross threaded:

20230624_083624.jpg


What was slightly alarming was the lack of sheathing on an earth cable in the side entry:

20230624_083905.jpg



I've put a sheathing on it for now as a temporary measure until its sorted properly. As I unscrewed it, it was pretty chewed up where it joined the earth bar also:

20230624_084122.jpg


I'll look into replacing the surface box based upon how long the cables are...
 

Attachments

  • 20230624_083900.jpg
    477.9 KB · Views: 16
I hate to say it, but looking at that chewed up earth, I fear every terminal was tightened with an impact driver. At an absolute minimum I'd turn the power off and look at the other CPC's (earth wires). If required trim them so you are biting on undamaged copper and loop the end around (similar to how the Neutral's are) so you get a better connection.
 
You would normally put the two lighting circuits on separate RCDs, so one RCD tripping doesn't plunge the whole house into darkness. But it could be done this way because of a borrowed neutral e.g. the landing light (L supplied from downstairs, N to upstairs) and they couldn't be bothered to fix that.
 
You would normally put the two lighting circuits on separate RCDs, so one RCD tripping doesn't plunge the whole house into darkness. But it could be done this way because of a borrowed neutral e.g. the landing light (L supplied from downstairs, N to upstairs) and they couldn't be bothered to fix that.
A borrowed neutral is required to be on one circuit rather than just one RCD though for safety reasons (which of course would no longer render it a borrowed neutral).
 
Pretty grim. I've spent time on it today to put new cables in and glands:

20230624_182602~2.jpg



Still not perfect but have addressed the side entry issues. Unfortunately the cables aren't long enough to allow the Wago junction box to be used correctly, what's the best way to resolve this, if any?


20230624_182440.jpg
 
Unfortunately the cables aren't long enough to allow the Wago junction box to be used correctly, what's the best way to resolve this, if any?
Without seeing it for myself this is a bit of a guess, but I'd probably grab a 20mm holesaw and make three or four holes holes is the back of the top of the Wago XL box near the top, mark everything with a Sharpie and then feed the short original wires through the back of the box, resulting in the short wires being nearer the top, and the box being mounted lower down.
When done you should fit cable ties so no one can easily unclip the front.

EDIT you may have to flip 180 degrees so the wago's are at the bottom, and the new cables enter at the top
 
Out of interest, if I ever upgraded to rcbo's, I'm assuming these are all single pole aside from the 'sockets first floor' because I've found this is actually incorrectly labeled and it's actually sockets for both floors with two cables entering the one mcb. Therefore it'd require a double pole rcbo?

...or is it simply wired like that as its a ring and not a radial, therefore still a single pole rcbo
 

Reply to Consumer unit extension wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had a consumer unit replacement today. It was a bit of a nightmare as most of the cables were too short for the new unit. I extended the ones...
Replies
24
Views
5K
I was just googling for skeleton boards after reading the last thread and various pictures of consumer units popped up, some wired terribly and...
Replies
6
Views
703
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
620
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock