Guest viewing is limited
K
Kev2632
Hello, i was doing an RCD test yesterday on half its rating, and the rcd kept tripping everytime, does this mean the RCD is faulty?
Best test it again with all MCB's switched off to get a better idea. It could well need replacing - they are not as reliable as people think
yea i did the ramp test and it tripped out at 17ma :s, there was some things plugged in at the time of the test happening yea?
It could be giving a bad reading then, For Example the things you still have connected could be producing earth leakage..
Therefore if its leaking 5ma then the 17 its tripping at will man 23ma
As above retest at RCD with no MCB'S ON
it's these 5 week courses. week 6 is when they were going to mention placing probes on live terminals.
Its also the case that some rcd's have remote C.T.'s and this must be tested downstream of these monitors this isnt usually found in domestic but more so commercial and industrial where rcd's monitor over 3ph, i understand this won't ever effect 99% of sparkies out there but just noting it so this thread isn't misleading in saying the RCD's should be tested at the terminals as on occasions this isnt the correct method.
Most Rcd 's are fine to test at terminals but some are designed in that the coil is connected after the live terminal thus using terminals for testing won't operate the device
Save me explaining it in full read this previous thread ...
.http://www.electriciansforums.net/i...stallations/28288-rcd-testing-no-trip-db.html
Only the one as far as i know. The manufacturers suggestion is to connect 10cm or so of conducters to the terminals and test from the ends these!!
There are plenty that use remote monitoring using current transformers, ive fitted them on occasion and many brands available and yes although this thread is really about Rcd's in standard consumer units i thought it deserves a mention that other rcd devices exist that cant be tested at the terminals in this manor but regarding AdieB noting the older MEM rcd's i believe these were the only one with this issue from a domestic CU point of view.
This type of Earth leakage protection where an external CT is used are termed as relay's. The smallest i've seen are 300mA, but most incorporate adjustable settings for both tripping values and time... You wouldn't use a standard RCD tester to test such relay's, a secondary injection test kit is a far more appropriate tool...
RCD tripping at half the rating ?
Kev2632,
Engineer54,
