K
Kev2632
Hello, i was doing an RCD test yesterday on half its rating, and the rcd kept tripping everytime, does this mean the RCD is faulty?
Discuss RCD tripping at half the rating ? in the UK Electrical Forum area at ElectriciansForums.net
it is faulty and requires replacing
Test at terminals of rcd
yea i did the ramp test and it tripped out at 17ma :s, there was some things plugged in at the time of the test happening yea?
oh ok yea, i didnt know if that was possible? i take it that is still ok to do yea?
Have they started teaching a different way to test a rcd now days then ?
Couldn't be anything else then?
of course but why mess change it and cure it
Oh Dear, ....It's statements like this that make me wonder what the hell's going on back in the UK these day's!!!
If the RCD is MEM then it will not test correctly from the rcd you have to test it downline.
AdieB
Never had a problem with them myself tbh can you explain a bit more.
Most Rcd 's are fine to test at terminals but some are designed in that the coil is connected after the live terminal thus using terminals for testing won't operate the device
Save me explaining it in full read this previous thread ...
.http://www.electriciansforums.net/i...stallations/28288-rcd-testing-no-trip-db.html
There are plenty that use remote monitoring using current transformers, ive fitted them on occasion and many brands available and yes although this thread is really about Rcd's in standard consumer units i thought it deserves a mention that other rcd devices exist that cant be tested at the terminals in this manor but regarding AdieB noting the older MEM rcd's i believe these were the only one with this issue from a domestic CU point of view.
Reply to RCD tripping at half the rating ? in the UK Electrical Forum area at ElectriciansForums.net