it's these 5 week courses. week 6 is when they were going to mention placing probes on live terminals.
 
If the RCD is MEM then it will not test correctly from the rcd you have to test it downline.
AdieB
 
As Darkwood says beet me to it . But I have also had no problem with the very latest MEM RCD's but have had a problem with the older units.
AdieB
 
Its also the case that some rcd's have remote C.T.'s and this must be tested downstream of these monitors this isnt usually found in domestic but more so commercial and industrial where rcd's monitor over 3ph, i understand this won't ever effect 99% of sparkies out there but just noting it so this thread isn't misleading in saying the RCD's should be tested at the terminals as on occasions this isnt the correct method.
 
Most Rcd 's are fine to test at terminals but some are designed in that the coil is connected after the live terminal thus using terminals for testing won't operate the device

Save me explaining it in full read this previous thread ...
.http://www.electriciansforums.net/i...stallations/28288-rcd-testing-no-trip-db.html


Only the one as far as i know. The manufacturers suggestion is to connect 10cm or so of conducters to the terminals and test from the ends these!!
 