Kitchen
Can see both ends of pipes i.e. one end into taps and one into plastic fitting at ground level.
Not necessary any longer due to RCD's
No - NOT 'Not necessary any longer due to RCD's' - Should NOT be bonded.
Bonding such isolated parts introduces a hazard.

Not necessary to remove as not a bathroom and irrelevant if supp bonding here goes back to MET or to light fitting, no gain no loss.
No (I didn't realise the kitchen had plastic supply as well) The bonding should be removed.
It's just that supplementary bonding is never required in a kitchen but this actually creates a hazard.

Bathroom
As per kitchen both ends of cold pipe visible i.e. one into plastic fitting at floor and one into taps
Same replies as the kitchen.

You said - "
If you can see both ends of the copper pipes and they are not connected electrically to anything else then they should not be bonded." - the cold pipe has a joint and then pipe running into an electric shower - a dumb question but would that count as electrically connected?​

That is a matter for interpretation.
If you or electrician think that the pipe entering the shower is an exposed conductive part and/or may become live by coming into contact with the shower's line conductor (in whatever circumstance) then the pipe should be earthed in the shower - to operate the mcb should this happen.


Am I looking to get this supp bonding removed or connected to all exposed conductive parts or does it makes no odds and leave as is?
It should be removed from any isolated parts.
These parts are not isolated at the moment because of the wrongly applied bonding.

​
 
To be honest, I'm not sure.

Even when the water is supplied in plastic the regs say to still bond on consumers side of stop-cock.
I suspect the regs haven't caught up with plastic gas supplies yet.

If both water and gas were supplied to your house in plastic and all pipes in the house were >500MΩ to MET would you want to connect them?

I know the pipes would still be connected to appliance CPCs and it would not apply so maybe continuing with main bonding is a way of ensuring there is some bonding.


The pipes in this thread, though, were not the supply pipes but short lengths between plastic and taps.
 
lobello you obviously have a lot of time on your hands at the moment so if you would like a bit of background reading have a look in the "17th edition fact sheet`s" thread at Fact Sheets 4 and 5. They cover Extraneous-conductive parts and Locations containing a bath or shower. Enjoy!

- - - Updated - - -

lobello you obviously have a lot of time on your hands at the moment so if you would like a bit of background reading have a look in the "17th edition fact sheet`s" thread at Fact Sheets 4 and 5. They cover Extraneous-conductive parts and Locations containing a bath or shower. Enjoy!
 