G
GLENNSPARK
read what you put then in red..
where doed it mention EIC eh?
where doed it mention EIC eh?
Referring to the OPs concern about continuity being broken by plastic lengths of pipe -
The purpose of bonding is not to maintain continuity and indeed plastic pipe feeding the basin copper pipes means that these copper pipes must NOT be bonded.
read what you put then in red..
where doed it mention EIC eh?
read what you put then in red..
where doed it mention EIC eh?
From your description, that is correct.The cold water pipes are in exactly the same scenario (plastic pipe out of concrete floor into copper pipe) and are bonded (supplementarily I think to the extractor and light in the bathroom but for all I know one or both of the green and yellows may go back to the MET).
So if the hot pipe must NOT be bonded then surely it would follow that neither must the cold?
That's the point - it does not say 'all pipework', it says 'all extraneous conductive parts'.t to omit supp bonding in a bathroom if all pipework is effectively bonded to the MET.
I would not think the CU replacement would involve checking "supplementary bonding was adequate" as none is now required.A little knowledge is a dangerous thing for sure...think I have to take the advice of trust the experts judgement - one who did the EICR and the other who did the resultant CU change and accompanying EIC. Both from my understanding have a duty to check both mains and supp bonding are adequate when doing the both the inspection and notifiable work.
No disrespect to you (I would not expect you to) but it is clear that you do not understand the purpose nor application of supplementary bonding.
Unfortunately, nor do a lot of 'electricians'.
From your description, that is correct.
That's the point - it does not say 'all pipework', it says 'all extraneous conductive parts'.
Pipes that are NOT e-c-ps must NOT be bonded.
I would not think the CU replacement would involve checking "supplementary bonding was adequate" as none is now required.
The EICR would report on the installation without altering anything.
From what you say it would appear that some doubts should have been raised about the supplementary bonding.
Supp bonding not required in kitchens anyway.Supp bonding to both hot and cold pipes and sink in the kitchen - 1 lead disappears into the wall.
If, as you said these pipes are supplied by plastic (and so NO continuity to anything else) then this 'bonding' (actually would be earthing, not bonding) should be removed.Supp bonding from cold pipe in bathroom - 2 leads disappear into the wall. None on hot water pipes in bathroom.
Supplementary bonding should not go to the MET.No way of me verifying if this supp bonding goes to a. the MET or b. any or a number of the appliances within the kitchen or bathroom. Or even in the case of the bathroom cold pipe one cable could go to MET and one to the light.
Can only be determined by testing as telectrix has said, although obviously any wire connections have to be disconnected.Additionally no idea if the possibly short run of plastic pipe (it disappears into concrete floor) is long enough to make the pipework in the bathroom or kitchen non-extraneous or if it remains extraneous.
There are a lot of variables. Even without your (now) RCD protection supplementary bonding may not be necessary.So many variables, what would be your advice - check back with the spark who did the EICR or the one who gave me the EIC, get another spark in. Or just trust it to have been assessed properly in the EICR.
No harm in keeping correctly applied bonding. Check 'isolated' parts.And if no supp bonding is actually required is there any harm in there being supp bonding in the bathroom or kitchen (as detailed above) if it runs to aplliances in thos rooms rather than the MET.
Supp bonding not required in kitchens anyway.
Could the one that disappears into the wall be Main Bond from water supply?
If, as you said these pipes are supplied by plastic (and so NO continuity to anything else) then this 'bonding' (actually would be earthing, not bonding) should be removed.
Supplementary bonding should not go to the MET.
It is to connect all extraneous and exposed conductive parts in a location (bathroom) to equalise any potential difference in the event of a fault - i.e. those parts becoming live.
So, perhaps you can see why any 'isolated' parts (sink pipes supplied by plastic, door handle or even a spoon) should NOT be bonded.
If there are any anomalies then I would not think calling the EICR one back would be wise.
Have a word with the CU installer.
Mmmm as I pointed out I typed EICR by mistake rather than EIC, just looking through the paperwork I realised it was an EIC hence marking that up for you. The electrician who did the CU change and provided the "EIC" actually said I'd get another EICR - the two cover pretty much exactly the same ground all be it from different Regulatory bodies - ECA and NIECEC.
Thanks for your input Glenn.
If im reading that as i think im reading that, then you're wrong lobello.
EIC and EICR are completley seperate certificates, and nothing to do with individual schemes. The EIC isn't just ECA and the EICR isn't just NICEIC.
Mark.
Correct1. Main bonding is just above the incoming water on/off in the immersion cupboard (in hall) and is 10mm. On an old test (back in the days of 16th - 2004) is listed as equipotential bonding to water mains. On recent EIC and EICR also identified as 10mm main protective bonding conductor to water.
Ok - not really needed.2. The one linking the cold to hot tap and kitchen sink - which goes back into wall behind and below the sink is (according to 2004 test) listed as 4mm supplementary bonding...
3. This test from 2004 didn't see the supp bonding in the bathroom, side of bath tough to remove! But I'm fairly sure this is also 4mm. Surprising he didn't see this as he originally fitted the shower (just above the bath taps) electrics with a plumber.
4. All this bonding was I assume done when the flats were built in 1996. Nothing altered bonding wise since I bought in 1998 and fairly sure previous owner did no work. So would be similar in 120 other flats.
If you can see both ends of the copper pipes and they are not connected electrically to anything else then they should not be bonded.Where the pipe comes up from the concrete floor it is plastic but then copper from there to taps. Where the pipes go into floor from the immersion cupboard it's all copper.
It's nothing to do with breaking the continuity. It would be better if all metal parts had the continuity broken.Guessing here but I think the actual pipe running under the floor is copper, the plastic was perhaps just an easy way for the original fitters to get the piping into room. Hence my original point wondering if a short run of plastic i.e. plastic bend would break the continuity back to the main bonding.
And shower when fitted.Makes sense at least for now ;-) Still given it's 4mm think it's probably connected to lights and extractor fan.
Oh well. Though, perhaps, he deserves a high price.CU installer - grumpy, defensive and very expensive. I may have burnt my bridges with him as booked in for appliance testing recently but a more reasonably priced decent option came up and cancelled. Not certain he'll provide answers but can try...he'd likely charge me £200 to check and remedy as well!
Unnecessary in the kitchen so it doesn't matter there.Guess the question now is assuming the pipes in kitchen and bathroom are connected to electrical fittings in those rooms and not the MET (as you say it ought not go back to MET and can't imagine they built 120 flats wrongly). Is there any issue with this or is it simply unnecessary.
He would have noticed it at the CU but may not have disconnected it.And finally at least for now, would assume the CU installer would know if the supp bonding went to the MET as he'd have to reconnect it when fitting the new CU??? If it doesn't go to the MET it has to go to the lights or other electrics in same room right?
Lobello I think you are getting your knickers in a twist over nothing.
5.You have EIC's and EICR's in place which covers your ---.
6.You need to get out more.
That is true as far as main bonding is concerned but there isn't really much point checking that which his work will render no longer relevant.None the less I'd consider that fitting a new CU would necessitate checking the bonding arrangements, my understanding is any Part P notifiable work would do this regardless. Especially changing the main board, fitting RCD's and all involved in that.
That is true as far as main bonding is concerned but there isn't really much point checking that which his work will render no longer relevant.