No - NOT 'Not necessary any longer due to RCD's' - Should NOT be bonded.Kitchen
Can see both ends of pipes i.e. one end into taps and one into plastic fitting at ground level.
Not necessary any longer due to RCD's
Bonding such isolated parts introduces a hazard.
No (I didn't realise the kitchen had plastic supply as well) The bonding should be removed.Not necessary to remove as not a bathroom and irrelevant if supp bonding here goes back to MET or to light fitting, no gain no loss.
It's just that supplementary bonding is never required in a kitchen but this actually creates a hazard.
Same replies as the kitchen.Bathroom
As per kitchen both ends of cold pipe visible i.e. one into plastic fitting at floor and one into taps
You said - "If you can see both ends of the copper pipes and they are not connected electrically to anything else then they should not be bonded." - the cold pipe has a joint and then pipe running into an electric shower - a dumb question but would that count as electrically connected?
That is a matter for interpretation.
If you or electrician think that the pipe entering the shower is an exposed conductive part and/or may become live by coming into contact with the shower's line conductor (in whatever circumstance) then the pipe should be earthed in the shower - to operate the mcb should this happen.
It should be removed from any isolated parts.Am I looking to get this supp bonding removed or connected to all exposed conductive parts or does it makes no odds and leave as is?
These parts are not isolated at the moment because of the wrongly applied bonding.