No disrespect to you (I would not expect you to) but it is clear that you do not understand the purpose nor application of supplementary bonding.
Unfortunately, nor do a lot of 'electricians'.
From your description, that is correct.
That's the point - it does not say 'all pipework', it says 'all extraneous conductive parts'.
Pipes that are NOT e-c-ps must NOT be bonded.
I would not think the CU replacement would involve checking "supplementary bonding was adequate" as none is now required.
The EICR would report on the installation without altering anything.
From what you say it would appear that some doubts should have been raised about the supplementary bonding.
No offence taken Geoff and your are correct.
The EICR and EIC have relevant boxes ticked for "Presence of supp bonding conductors".
Situation is...
Supp bonding to both hot and cold pipes and sink in the kitchen - 1 lead disappears into the wall.
Supp bonding from cold pipe in bathroom - 2 leads disappear into the wall. None on hot water pipes in bathroom.
No way of me verifying if this supp bonding goes to a. the MET or b. any or a number of the appliances within the kitchen or bathroom. Or even in the case of the bathroom cold pipe one cable could go to MET and one to the light.
Additionally no idea if the possibly short run of plastic pipe (it disappears into concrete floor) is long enough to make the pipework in the bathroom or kitchen non-extraneous or if it remains extraneous.
So many variables, what would be your advice - check back with the spark who did the EICR or the one who gave me the EIC, get another spark in. Or just trust it to have been assessed properly in the EICR.
And if no supp bonding is actually required is there any harm in there being supp bonding in the bathroom or kitchen (as detailed above) if it runs to aplliances in thos rooms rather than the MET.
Supp bonding not required in kitchens anyway.
Could the one that disappears into the wall be Main Bond from water supply?
If, as you said these pipes are supplied by plastic (and so NO continuity to anything else) then this 'bonding' (actually would be earthing, not bonding) should be removed.
Supplementary bonding should not go to the MET.
It is to connect all extraneous and exposed conductive parts in a location (bathroom) to equalise any potential difference in the event of a fault - i.e. those parts becoming live.
So, perhaps you can see why any 'isolated' parts (sink pipes supplied by plastic, door handle or even a spoon) should NOT be bonded.
Can only be determined by testing as telectrix has said, although obviously any wire connections have to be disconnected.
There are a lot of variables. Even without your (now) RCD protection supplementary bonding may not be necessary.
It is not a question of "metal pipe - apply bonding"
If there are any anomalies then I would not think calling the EICR one back would be wise.
Have a word with the CU installer.
No harm in keeping correctly applied bonding. Check 'isolated' parts.
It should not run to MET.
There was no need for it in kitchens anyway.
Thanks Geoff
1. Main bonding is just above the incoming water on/off in the immersion cupboard (in hall) and is 10mm. On an old test (back in the days of 16th - 2004) is listed as equipotential bonding to water mains. On recent EIC and EICR also identified as 10mm main protective bonding conductor to water.
2. The one linking the cold to hot tap and kitchen sink - which goes back into wall behind and below the sink is (according to 2004 test) listed as 4mm supplementary bonding...
3. This test from 2004 didn't see the supp bonding in the bathroom, side of bath tough to remove! But I'm fairly sure this is also 4mm. Surprising he didn't see this as he originally fitted the shower (just above the bath taps) electrics with a plumber.
4. All this bonding was I assume done when the flats were built in 1996. Nothing altered bonding wise since I bought in 1998 and fairly sure previous owner did no work. So would be similar in 120 other flats.
Where the pipe comes up from the concrete floor it is plastic but then copper from there to taps. Where the pipes go into floor from the immersion cupboard it's all copper. Guessing here but I think the actual pipe running under the floor is copper, the plastic was perhaps just an easy way for the original fitters to get the piping into room. Hence my original point wondering if a short run of plastic i.e. plastic bend would break the continuity back to the main bonding.
Makes sense at least for now ;-) Still given it's 4mm think it's probably connected to lights and extractor fan.
CU installer - grumpy, defensive and very expensive. I may have burnt my bridges with him as booked in for appliance testing recently but a more reasonably priced decent option came up and cancelled. Not certain he'll provide answers but can try...he'd likely charge me £200 to check and remedy as well!
Guess the question now is assuming the pipes in kitchen and bathroom are connected to electrical fittings in those rooms and not the MET (as you say it ought not go back to MET and can't imagine they built 120 flats wrongly). Is there any issue with this or is it simply unnecessary.
And finally at least for now, would assume the CU installer would know if the supp bonding went to the MET as he'd have to reconnect it when fitting the new CU??? If it doesn't go to the MET it has to go to the lights or other electrics in same room right?
Thanks again.
Lobello I think you are getting your knickers in a twist over nothing.
1.Main bonding in place and adequate.
2.All circuits RCD protected.
3.Presence of at least some supplementary bonding in the bathroom.....in practice whether it goes to the MET or more correctly to exposed conductive parts within the location it will do the same job.
4.It most likely isnt even required.
5.You have EIC's and EICR's in place which covers your ---.
6.You need to get out more.
Reactions: 3 people
Mmmm as I pointed out I typed EICR by mistake rather than EIC, just looking through the paperwork I realised it was an EIC hence marking that up for you. The electrician who did the CU change and provided the "EIC" actually said I'd get another EICR - the two cover pretty much exactly the same ground all be it from different Regulatory bodies - ECA and NIECEC.
Thanks for your input Glenn.
If im reading that as i think im reading that, then you're wrong lobello.
EIC and EICR are completley seperate certificates, and nothing to do with individual schemes. The EIC isn't just ECA and the EICR isn't just NICEIC.
Mark.
Mark.
Thanks Mark yes I *now* realise they are different certificates.
You read that particular quote wrongly, I was marking up that I knew they were different certificates.Didn't phrase it well though.
My confusion caused initially by the ECA guy who fitted the new CU that he would provide a new EICR.
None the less I'd consider that fitting a new CU would necessitate checking the bonding arrangements, my understanding is any Part P notifiable work would do this regardless. Especially changing the main board, fitting RCD's and all involved in that.
Looking through the paperwork earlier I identified my mistake
Correct
Ok - not really needed.
If you can see both ends of the copper pipes and they are not connected electrically to anything else then they should not be bonded.
It's nothing to do with breaking the continuity. It would be better if all metal parts had the continuity broken.
Supplementary bonding is applied to reduce the resistance between parts which already have continuity.
And shower when fitted.
Oh well. Though, perhaps, he deserves a high price.
Unnecessary in the kitchen so it doesn't matter there.
In the bathroom it should have connected all extraneous and exposed conductive parts together but not isolated parts.
In the past people tended to connect everything 'just in case' without having to think about it.
He would have noticed it at the CU but may not have disconnected it.
5. True but I'm over conscientious and a obsessive/profound worrier ;-0
6. Too true but in my defence I have a flu like virus right now and hence stuck indoors
That is true as far as main bonding is concerned but there isn't really much point checking that which his work will render no longer relevant.
Geoff your being extremely helpful thank you.
Let me see if I can get this straight so as to talk to the CU installer with minimum fuss...Is below correct..
Kitchen
Can see both ends of pipes i.e. one end into taps and one into plastic fitting at ground level.
Not necessary any longer due to RCD's
Not necessary to remove as not a bathroom and irrelevant if supp bonding here goes back to MET or to light fitting, no gain no loss.
Bathroom
As per kitchen both ends of cold pipe visible i.e. one into plastic fitting at floor and one into taps
You said - "
If you can see both ends of the copper pipes and they are not connected electrically to anything else then they should not be bonded." - the cold pipe has a joint and then pipe running into an electric shower - a dumb question but would that count as electrically connected?
Am I looking to get this supp bonding removed or connected to all exposed conductive parts or does it makes no odds and leave as is?
Kitchen
No - NOT 'Not necessary any longer due to RCD's' - Should NOT be bonded.
Bonding such isolated parts introduces a hazard.
No (I didn't realise the kitchen had plastic supply as well) The bonding should be removed.
It's just that supplementary bonding is never required in a kitchen but this actually creates a hazard.
Bathroom
Same replies as the kitchen.
You said - "
That is a matter for interpretation.
If you or electrician think that the pipe entering the shower is an exposed conductive part and/or may become live by coming into contact with the shower's line conductor (in whatever circumstance) then the pipe should be earthed in the shower - to operate the mcb should this happen.
It should be removed from any isolated parts.
These parts are not isolated at the moment because of the wrongly applied bonding.
So why does it say bond gas@ meter box even tho it comes in from street in plastic
Then changes to copper to go to combi ..
To be honest, I'm not sure.
Even when the water is supplied in plastic the regs say to still bond on consumers side of stop-cock.
I suspect the regs haven't caught up with plastic gas supplies yet.
If both water and gas were supplied to your house in plastic and all pipes in the house were >500MΩ to MET would you want to connect them?
I know the pipes would still be connected to appliance CPCs and it would not apply so maybe continuing with main bonding is a way of ensuring there is some bonding.
The pipes in this thread, though, were not the supply pipes but short lengths between plastic and taps.
lobello you obviously have a lot of time on your hands at the moment so if you would like a bit of background reading have a look in the "17th edition fact sheet`s" thread at Fact Sheets 4 and 5. They cover Extraneous-conductive parts and Locations containing a bath or shower. Enjoy!
- - - Updated - - -
Supplementary bonding required with RCD's?
lobello,
Top Cat,