The 100 and 200 ohm values that are thrown about by the NICEIC and BS7671 are one almighty joke
Although we may disagree on one or two issues regarding TT systems I have the upmost admiration for your passion towards them

The 100 and 200 ohm values that are thrown about by the NICEIC and BS7671 are one almighty joke

6 Hours later!! lol!!
Another Reg bible basher!! with no understanding of a TT system!!
21 ohms is the max for sub-station earthing and the like, but you'll never see a value anywhere near that high at a sub-station.
The 100 and 200 ohm values that are thrown about by the NICEIC and BS7671 are one almighty joke, and good for basically nothing!! Always aim for a low double figure. the old accepted standard was 10 ohms, but that was with decent sized and lengths of earth rods. Just as important as low Ra values is the stability of the earth rod position(s) The deeper the better, for both stability and Ra values...
Although we may disagree on one or two issues regarding TT systems I have the upmost admiration for your passion towards them![]()
Sorry bud, I'm with Wirepuller. RCBO on every circuit and an up front S type and I couldn't give a monkeys about the Ra as long as it will stay under 1667 ohms.
At least wirepuller knows what he's doing
Pardon ???? I haven't and never have said that at all!! I'm basically saying you shouldn't ever rely on a single RCD device on a TT system. Basically because they are still not that a reliable device!!
Sorry bud, I'm with Wirepuller. RCBO on every circuit and an up front S type and I couldn't give a monkeys about the Ra as long as it will stay under 1667 ohms.
I'm with you on this...only thing I would add is that an S type up front would normally be 100ma....so you'd need 500 ohms max.