6 Hours later!! lol!!




Another Reg bible basher!! with no understanding of a TT system!!




21 ohms is the max for sub-station earthing and the like, but you'll never see a value anywhere near that high at a sub-station.

The 100 and 200 ohm values that are thrown about by the NICEIC and BS7671 are one almighty joke, and good for basically nothing!! Always aim for a low double figure. the old accepted standard was 10 ohms, but that was with decent sized and lengths of earth rods. Just as important as low Ra values is the stability of the earth rod position(s) The deeper the better, for both stability and Ra values...

Ok...low double figures...say 12 ohms= PEFC of 19 amps

Time to operate a 6a type B mcb.....30s
time to operate a 10a type B mcb....190s
time to operate a 16a type B mcb....hours
time to operate a 32a type B mcb....it wont
time to operate a 30ma RCD.....2-300ms max

Ra of 200-1667 ohms
time to operate a 30ma RCD.....2-300ms max

So unless you've got a CU full of 6/10/16a devices (lets just forget the 32's ,they dont matter)and are happy to wait from half a minute to several hours for one to trip if the RCD fails 12 ohms is just as 'nunpty' as 200 ohms.
 
Last edited by a moderator:
Got my wires crossed I've been spouting on about the earth rod resistance.
And yes we were always told to inform dno if ra at premisis was higher than 21 ohms which in turn affected the psc.
 
@ E54
Following on from post #17. A while back I promised I'd not get involved in another TT Ra 'debate'...but the logic still defeats me. As My views are in a clear minority on here I'd like to understand...I really would.
So perhaps you could explain why a CU with all 32a OCPD devices in it and 30ma RCD protected would be good with a 'low double figure' Ra but 'numpty' with a sub 200 ohms Ra?
What does the 12 ohm Ra do that the sub 200 ohm Ra doesnt?
I'm not having a go here,or wanting to get into another pointless row.....but this still defeats me.
 
Going by your figures, you have in a way answered your own question to a point, at the very least the lower rated protective devices WILL trip!! (So the lower you get your Ra value down, the better and it's not always the chore it's made out to be!!) Maybe not in the desired times but they will trip!! Absolutely no chance whatsoever with either 100/200ohms suggested by others. Combine a decent low double figure Ra with decent bonding at the MET and your overall Zs could well improve further to trip out a 32A breaker. Now if i had driven a rod in the ground and achieved an Ra of 10/12 ohm, i'd be, without any thought whatsoever, adding another rod on top Knowing full well that my Ra value will almost halve again, and ''continue to improve''!! And we haven't even talked about system stability, that your rarely achieve with a single 1.2m rod of any size, especially in some of the soil conditions found in parts of the UK.

Most here only look directly at the Ra figure they attain at time of installation, which is fine to a point, but with a deep driven rod, that value will continue to decrease over a given time period as the soil consolidates around the rod and connections. My system for instance, was around 5 to 6 ohms mark when the overall system was completed. I am now at a sub 0 ohm value, 3 years or so later (checked/measured just last week) and my ground/soil conditions are far, far from ideal i can tell you!! ...lol!!

The only reason i can see for the old standard 10 ohm for a TT system being left behind, is the advent of RCD devices, which is all fine and dandy till the things fail for one reason or another and your left with this numpty 100/200 ohm as your earth fault protection. Which comes to the point where we DO agree, that TT systems should have an up-front additional S type protection to cater for such failures of single RCD devices.

No other country that i know of, has a standard anywhere near that of what the UK (IET) suggests, even the Yanks want top see a 20 ohm Ra, and if it's higher another rod is to be installed. (and the Yanks (god bless them) use 3/4'' 10 foot rods, not 3/8'' 4 footers as you have in the UK!!) and many more still use what we used to have, 10 ohms!! I think that is the recognised value in S Africa too, pretty sure Marvo has stated this figure in past Threads. And he, as i remember often has to use several coupled rods in his sandy soil conditions!! He still uses RCD protection, so what's so different in the UK having to comply with realistic Ra values on TT systems??
Now if all these other countries sensible standards don't or can't convince you, then just stick to your die hard support of IET's numbty 200 ohms!! lol!!
 
Although we may disagree on one or two issues regarding TT systems I have the upmost admiration for your passion towards them :D

That's not quite true, i would always prefer to see a TN system over a stand alone TT system, and always advise whenever possible to obtain a PME connection from the DNO!! Where a TT system is the only choice you have, then it should be taken seriously, and installed to the very best standard of protection you can achieve. And that isn't banging in a single short twig like rod in the ground and thinking that 200 ohms is a good-un!! It isn't, hasn't, and never will be any good to man nor beast!! My passion, as you call it, is for doing things properly, from knowing what i'm doing and why i'm doing it, which seems to be totally lacking in the UK these day's, especially when it comes to TT systems....
 
Sorry bud, I'm with Wirepuller. RCBO on every circuit and an up front S type and I couldn't give a monkeys about the Ra as long as it will stay under 1667 ohms.
 
Eng54 why do you prefer MCBs over RCDS I mean at least you can test a RCD.....can't see why using a RCD for fault protection is so bad maybe you can explain ?
 
Sorry bud, I'm with Wirepuller. RCBO on every circuit and an up front S type and I couldn't give a monkeys about the Ra as long as it will stay under 1667 ohms.

Very professional of you!!

Of course your with wirepuller, it means you don't have to know how or why, and therefore don't have to give a dam either!! At least wirepuller knows what he's doing, whether we agree to disagree or not, and i doubt very much if he would agree with your last statement!!
 
Pardon ???? I haven't and never have said that at all!! I'm basically saying you shouldn't ever rely on a single RCD device on a TT system. Basically because they are still not that a reliable device!!
 
At least wirepuller knows what he's doing

And I don't?!

Listen pal, I agree wholeheartedly that achieveing TN values on TT systems is a far better way to do it that to rely on RCDs for fault protection. If every customer I had was willing to pay for me to achieve sub 1ohm values then I would but this isn't going to be the case is it, so my point is, if you have to rely on RCD protection then why the hell does it matter what your Ra value is as long as you can guaruntee it will not go above 1667 ohms and you are not relying on a sole RCD.
 
Pardon ???? I haven't and never have said that at all!! I'm basically saying you shouldn't ever rely on a single RCD device on a TT system. Basically because they are still not that a reliable device!!

Sorry it just sound to me you "basically" dislike using RCDS as fault protection on TT systems, so if you take a low double figure RA reading how do you know it is going to stay that way throughout the year and also I hear a lot of doubt regarding the reliability of RCDS which is strange because how many of those OCPDs have you tested for reliability??........btw I'm not looking for a row just your perspective

Thanks
 
Last edited by a moderator:
Hmmm....thanks for the constructive reply E54......however I'm not persuaded. Get a TN value of Ra and I'm with you all the way. 10 ohms + and I'm with Skelton,I really cant see what difference it makes.
 
Sorry bud, I'm with Wirepuller. RCBO on every circuit and an up front S type and I couldn't give a monkeys about the Ra as long as it will stay under 1667 ohms.

I'm with you on this...only thing I would add is that an S type up front would normally be 100ma....so you'd need 500 ohms max.
 