Hi all

Got the below today.

Dilog DL6507. Buy online or call

Can see the massive benefit of these meters but never used one before. After doing some research some people seem to say clamp both tails and overs say clamp the earth.

What do you think is best and can you advise any tips with using one or false reading to look out for.

Thanks
 
I prefer clamping both of the tails, as this will show the leakage present in the installation.

Clamping the Earth can lead to misleading imported readings on TNC-S supplies where it is common to find tens' if not hundreds of mA of circulating earth currents sloshing around from other users of the network.
 
Thank you spark 68. I have a job tomorrow that has nuisance rcd tripping so I will have a play with it there.
 
I bought the Metrel Tek775 mini leakage clamp tester at the Elex show today as I thought it would be handy to have one.. it costs £40 cash total!! anyone else used one? what are they like?
 
I bought the Metrel Tek775 mini leakage clamp tester at the Elex show today as I thought it would be handy to have one.. it costs £40 cash total!! anyone else used one? what are they like?

Is it any good? its the cheapest earth leakage meter ive seen and wondered if that is reflected in the quality
 
Is it any good? its the cheapest earth leakage meter ive seen and wondered if that is reflected in the quality

The resolution is pants, for an earth leakage tester, and why it's probably so cheap!! The Dilog is a far better buy all round!!
 
The resolution is pants, for an earth leakage tester, and why it's probably so cheap!! The Dilog is a far better buy all round!!

why do you need a resolution better than 1mA when you are looking for leakage in the range 1mA upwards to 30mA or 100mA?
 
I think the better resolution would help to see if there is an upward or downward trend and the accuracy probably wouldn't be too hot at the low end of the scale so if you're checking a lot of individual appliances each with a small amount of leakage then the results may not be too accurate especially if you're adding them up and compounding the errors. I would pay the extra but I'm sure the lower res tester would be very usable if you understand the limitations and perfectly fine for global leakage testing, I suppose it depends mostly on budget.
 
I think the better resolution would help to see if there is an upward or downward trend and the accuracy probably wouldn't be too hot at the low end of the scale so if you're checking a lot of individual appliances each with a small amount of leakage then the results may not be too accurate especially if you're adding them up and compounding the errors. I would pay the extra but I'm sure the lower res tester would be very usable if you understand the limitations and perfectly fine for global leakage testing, I suppose it depends mostly on budget.

Couldn't of put it better, ...lol!! Plus i wouldn't be putting too much faith in a 40 quid leakage tester. If you need one (and in this day of reliance on RCD's you do...) far better to spend the extra and have a unit that can cover most, if not all of the likely situations you may encounter..
 
So the concencus is buy the dialog then. Looks like im getting a new gadget.

That, or the TM-EL9809 Earth Leakage Clamp Meter, which is a re-badged Dilog DL 6507!! You can get a 5% forum discount from the forum sponsor at testmeter.co.uk
 
That, or the TM-EL9809 Earth Leakage Clamp Meter, which is a re-badged Dilog DL 6507!! You can get a 5% forum discount from the forum sponsor at testmeter.co.uk

I forgot about that one, ive seen good reviews about it. And its cheaper than the dilog branded one.

Cheers,
Tim
 
That, or the TM-EL9809 Earth Leakage Clamp Meter, which is a re-badged Dilog DL 6507!! You can get a 5% forum discount from the forum sponsor at testmeter.co.uk

That's what I use, looked at Meggar, Kewtechnic and seaward units, but they are 2-5 times the price of the TM and it does the same job...good kit.
 
I'd post this in the trainee section if I had access (but I don't). I understand on the basics on why the "circulating earth currents" are there, but not fully grasping why they are not dangerous and not corresponding to a shock hazard off bonded metalwork etc.

In the spirit of the forum, I don't expect to be spoon fed the answer, but if someone could start me on the right track I'd be massively grateful.

I prefer clamping both of the tails, as this will show the leakage present in the installation.

Clamping the Earth can lead to misleading imported readings on TNC-S supplies where it is common to find tens' if not hundreds of mA of circulating earth currents sloshing around from other users of the network.
 