Discuss MICC Cable - phase to earth fault in the UK Electrical Forum area at ElectriciansForums.net
Hello Gents,
I have a low IR reading on a lighting circuit - the circuit is 50 years old - i believe the fault is at the pot connection as there has been a downpour of water on this connection - I was going strip back the sheath and identify the point where the IR reading high - I was looking to connect the cable to an adaptable box , and then connect the outgoing from the box with FP 200 - Problem is I am struggling obtain an imperial pot to gland off at box - is there anything on the market that will enable me to connect the MICC cable into an adaptable box which will 1) maintain my earth continuity and 2) prevent any further moisture ingress in the existing healthy cable.
Sparky 63
Hello Gents,
Sparky 63
If this circuit is 50 years old I doubt very much that this will be the cause if it was well made off at the installation date unless someone without proper knowledge has been buggering about with it.
As has been suggested, get a heat gun on it.
and tell us the IR reading that you consider low.
The really old smaller size cables I have come across quite often are difficult to work with , as they are very small and if buried in the wall have been prone to corrosive reaction with the cement and plaster , so I would be careful with them ,,,,
be fair. he might have needed to go to the offy for beer. :26:
First you do as said in previous posts, if this doesn't help, then get the size of the cable by looking on the pot for a number, see if there is a compatible size in metric, or source a pot that fits.
If you are unsuccessful then as the end is no good cut it off. Now the tricky part. Carefully dismantle the pot assembly, cleaning all parts carefully, make sure you get the three indentations out where the disc sits you can then re-use the pot and use new compound and a new disc. You should have a good termination It can be done, I have had to do it.
Reply to MICC Cable - phase to earth fault in the UK Electrical Forum area at ElectriciansForums.net
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hi gentlemen, I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...