But is it still being termed "non standard" I have used it in the past, but I cant find much in the way of a defining answer, can we use it for subs or not I have to go up a floor on a refurb with about 10 90 degree turns to get to the sub, it would be ideal, its on tray the whole way and one tnuc of a wrestling match with swa
P
 
What ? not one of the 70 odd views have an opinion, I have posed it as a Q on the NICEIC Tech helpline I will post the answer here later
 
Why can’t you use double insulated if it’s a refurb you must be able run it on the tray installed.
SY cable is not for sub mains, not recognised in the regs.
How would you confirm the earthing conductor to the new DB meets the requirements.
My thoughts on the question, with the information provided.
 
That's the sort of thing I want to find out its got a bs number so I'll have to get in touch with a manufacturer for ccc etc
 
Why not a heavy duty flexible cable like H07RNF? The only differences really are the lack of screening (which presumably isn't required) and full compliance with bs7671.
 
  • Like
Reactions: the pict
I’m pretty sure there is an actual reg forbidding it’s use in bs7671 I haven’t got my regs book to hand at the moment but I’ll look when I’m in the office tomorrow.....
 
  • Like
Reactions: the pict
There aren't any regulations which prohibit specific materials, they only make requirements about complying with British standards
Check the on site guide then..... this is from an older version but it’s probably just as correct today well maybe not on the page number
F14A17C4-8688-440D-AF95-2AF96427B8CE.jpeg
 
  • Like
Reactions: the pict
Just to be pedantic, the onsite guide is a guide that only discourages the use of SY.

It is not a statute law forbidding the use of SY.
I agree but read a little more into why the OSG says this....
 
All I would say is use it at your peril....
 
  • Like
Reactions: the pict
What ? not one of the 70 odd views have an opinion, I have posed it as a Q on the NICEIC Tech helpline I will post the answer here later
It was Sunday we were all hungover and waiting on Sunday dinner :p
 
  • Like
Reactions: the pict
Check the on site guide then..... this is from an older version but it’s probably just as correct today well maybe not on the page number
View attachment 46018

The on site guide is not the regulation, it is a guide to the regulations.

I stand by my point that the regulations do not ban specific materials, they specify the standards to which the materials must comply.

I'm not suggesting that SY is ever compliant, just that it is wrong to say that it is specifically prohibited by the regulations.
 
The on site guide is not the regulation, it is a guide to the regulations.

I stand by my point that the regulations do not ban specific materials, they specify the standards to which the materials must comply.

I'm not suggesting that SY is ever compliant, just that it is wrong to say that it is specifically prohibited by the regulations.
I agree with you Dave I was mistaken and thought it was in the BYB or BBB when it was actually the little one. Sod using it though if the OSG says that which is published by the very organisation which publishes bs7671 id err on the side of caution.....
 
  • Like
Reactions: the pict
There is nothing wrong with using non BS cable but you have to justify its use and provide a full risk assessment and detail it's suitability for it's use.. it's not worth the extra paper and research if other compliant solutions exist, why do you need a screened cable out of interest?
 
  • Agree
Reactions: MFS Electrical
There is nothing wrong with using non BS cable but you have to justify its use and provide a full risk assessment and detail it's suitability for it's use.. it's not worth the extra paper and research if other compliant solutions exist, why do you need a screened cable out of interest?
 
  • Like
Reactions: the pict
There is nothing wrong with using non BS cable but you have to justify its use and provide a full risk assessment and detail it's suitability for it's use.. it's not worth the extra paper and research if other compliant solutions exist, why do you need a screened cable out of interest?

From the OP I get the impression that it is not the screening which he seeks but the easy availability and ease of installation (AKA sheer laziness)
 
In my defence its not lazyness its radius, ????? I will let you figure that out
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

the pict

Mentor
~
Joined
Location
Brodick
Business Name
Devlin Maguire Electrical

Thread Information

Title
SY Control Cable LSZH to BS EN 50525-3-11 and VDE 0250
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
19

Thread Tags

Advert

Thread statistics

Created
the pict,
Last reply from
the pict,
Replies
19
Views
2,627

Advert