I’ve not untangled it all yet. I’ve got a number of points from this inspection and the list of remedial work keeps growing.Is the heavily taped up cpc of the blue/brown T&E disappearing into the ceiling being used as a perm. live/switched live to the fan?
....and there is a socket being spurred off the shower so far.![]()
Sounds pretty poor.
However, open question to everyone, just what exactly would be wrong with taking a socket outlet off the shower circuit (or anything else such as ufh, or similar); if electrically it had the usual stuff right such as rcd, Zs within limits etc.
General question on people's thoughts about this.
You can’t run a 2.5mm spur from a 32A 6mm shower.Sounds pretty poor.
However, open question to everyone, just what exactly would be wrong with taking a socket outlet off the shower circuit (or anything else such as ufh, or similar); if electrically it had the usual stuff right such as rcd, Zs within limits etc.
General question on people's thoughts about this.
You can’t run a 2.5mm spur from a 32A 6mm shower.
Not matter what the Zs is. The cable is only rated at max 27A.
So unless you ran it in 6mm, which would be some effort for a 2g socketthen it’s not going to be compliant.
You can’t run a 2.5mm spur from a 32A 6mm shower.
Not matter what the Zs is. The cable is only rated at max 27A.
So unless you ran it in 6mm, which would be some effort for a 2g socketthen it’s not going to be compliant.
That is exactly what my head said at first too.
But....
Overload protection - each appliance protected by 13A fuse in plug. OK, two at once would be a bit interesting but unlikely.
(In some circumstances overload protection is allowed downstream - I'd need to read that bit again to comment further.)
Fault protection - it's RCD protected.
It's a truly horrible design but is it actually non-compliant?
That makes the upstream 32A MCB more likely to trip, and the spur is only drawing the heater current?What about shower running at same time as someone has plugged a heater in?
The breaker and 1st leg of 6mm to shower are correctly matched, so any overload here is dealt with normally by 32A breaker tripping.What about shower running at same time as someone has plugged a heater in?
That makes the upstream 32A MCB more likely to trip, and the spur is only drawing the heater current?
If it was ran in 6mm then technically it could be safe.
But as far as I’m aware a shower has to be a dedicated circuit and nothing else on it.
I don’t know if it does. When I rang NAPIT the chap I spoke to said it should be a dedicated circuit.Which reg covers that?
As a B32 wouldn't trip at all with a load of ~46 amps, the question is how hot does the 6mm get for the duration of the shower.Im just thinking, if the shower and heater together were above the MCB rating, but not enough to trip it. Just thinking out loud.
I agree that angle needs exploring, what requires a dedicated circuit. Appendix 15 comes to mind, but I don't have book here.But as far as I’m aware a shower has to be a dedicated circuit and nothing else on it.
Last week NAPIT told me "not to worry" about an RCD taking 0.5 seconds to trip due to a PV system back-feeding and not shutting down very quickly.When I rang NAPIT
As a B32 wouldn't trip at all with a load of ~46 amps, the question is how hot does the 6mm get for the duration of the shower.
It would trip after roughly 15 minutes with a 50A load.
We need someone to plug an EV into the other side of the socket!
I agree that angle needs exploring, what requires a dedicated circuit. Appendix 15 comes to mind, but I don't have book here.
If it is electrically sound then to me the problem it sort of violates the "principle of least surprise" in that you might have a lone socket that is still powered when someone thinks they have isolated the RFC/radials related to that.However, open question to everyone, just what exactly would be wrong with taking a socket outlet off the shower circuit (or anything else such as ufh, or similar); if electrically it had the usual stuff right such as rcd, Zs within limits etc.
General question on people's thoughts about this.
I’m not sure you can make a sweeping statement like that.If NAPIT or any scheme for that matter say it is okay then there is your answer, it probably isn't okay.
Nope, 2.5mm^2 would be fine, the maximum load could only be 26A max for a double socket outlet, and realistically 20A , so some if not most installation methods would have the capacity, exactly the same as a spur off a RFC.You can’t run a 2.5mm spur from a 32A 6mm shower.
Not matter what the Zs is. The cable is only rated at max 27A.
So unless you ran it in 6mm, which would be some effort for a 2g socketthen it’s not going to be compliant.
The way I’ve always had it explained to me is that a spur off a RFC is fine because they’re in a ring and the socket won’t pull more than 26A. This is assuming cable is clipped direct.Nope, 2.5mm^2 would be fine, the maximum load could only be 26A max for a double socket outlet, and realistically 20A , so some if not most installation methods would have the capacity, exactly the same as a spur off a RFC.
Would not have to be 6, or 4mm^2, and if it was a single socket or FCU probably 1.5mm^2 would be ok from a load perspective.
I ask the question, because one's initial thought is to object, but is it actually wrong?
I know it's unusual and unexpected, but perhaps more compliant and less unexpected than some things we see!
Not for a single or double socket as they have the 13A fuses limiting long-term loads to 13/26A (in fact most double sockets are only rated at 20A by specification).However for, in this case, a shower circuit it’s not in a ring so the full load of 32A can go down it and overload the 2.5mm.
...What starts as a single/double socket spurred off might then be spurred again like a radial but now violating the '2.5mm on 32A safe due to loop' aspect.
The way I’ve always had it explained to me is that a spur off a RFC is fine because they’re in a ring and the socket won’t pull more than 26A. This is assuming cable is clipped direct.
However for, in this case, a shower circuit it’s not in a ring so the full load of 32A can go down it and overload the 2.5mm.
More than happy to hear other explanations and I’ve got my annual assessment next month so I’ll make a point of asking about this very scenario with the assessor as it will be interesting to see what their take on it is.
If we have to find regs to justify the general feeling of unease then:So is compliant - why do we object?
So is compliant - why do we object?
Especially monks & nuns!Not usual practice and people are creatures of habit.
Especially monks & nuns!
You've got me thinking - why do I hate it? I think it's because I have a sixth sense that the unusual nature of it could create safety issues, as others have said too. Hopefully not for sparks, though we do all make mistakes sometimes especially when tired. I'm thinking more of the DIY hero, or those that know enough to be dangerous.What is the reason we try to find objections?
I agree that many of us would go into knee jerk mode when presented with a situation that is out of the ordinary, and condemn it without thinking.As I said in my statement of the question, cable sizing, protective device sizing, Zs, rcd, ads etc being OK.
(The question is equally applicable to an fcu with a 1A fuse added to a 7.5kw shower supplied via a 40A mcb - with 10mm^2 cable)
What is the reason we try to find objections?