Afternoon all been a while since I've posted.


at today's job I noticed 10mm meter tails with 6mm bonding and although my first thoughts were tails should be min 16mm and bonding 10mm

so at the risk of sounding stupid I couldn't find the exact reason why this was wrong as the 10mm would take 61amps

could anyone clear this for me?
 
Bonding is under sized, though it probably complied at the time of design/construction.
Nothing wrong with the CSA of the tails as far as BS7671 is concerned, though they are probably not double insulated.
 
Last edited by a moderator:
PVC insulated and sheathed I think you'll find, often referred to as DI though, but not strictly correct. A bit like calling a vacuum cleaner a hoover....everyone knows what it means even if it's not strictly correct.
 
Whether a cable is described as being double insulated, has no bearing on whether it is or isn't as far as BS7671 is concerned.
What matters is whether the cable complies with the requirements.
As cables with insulation and sheaths, and cables with reinforced insulation satisfy the requirements for double insulation, such cables are deemed as being double insulated.

Risterd despite your obsessive compulsion to disagree with me at every opportunity, I suggest that if you do not like my use of the term 'double insulation' for cables that satisfy the requirements for double insulation, that rather than continue this childish sniping at me across various forums, you take this particular matter up with the JPEL 64 committee.
By all means continue chasing after me, if that floats your boat.
 
Last edited by a moderator:
Whether a cable is described as being double insulated, has no bearing on whether it is or isn't as far as BS7671 is concerned.
What matters is whether the cable complies with the requirements.
As cables with insulation and sheaths, and cables with reinforced insulation satisfy the requirements for double insulation, such cables are deemed as being double insulated.

Risterd despite your obsessive compulsion to disagree with me at every opportunity, I suggest that if you do not like my use of the term 'double insulation' for cables that satisfy the requirements for double insulation, that rather than continue this childish sniping at me across various forums, you take this particular matter up with the JPEL 64 committee.
By all means continue chasing after me, if that floats your boat.

girls,girls!
 
Afternoon all been a while since I've posted.


at today's job I noticed 10mm meter tails with 6mm bonding and although my first thoughts were tails should be min 16mm and bonding 10mm

so at the risk of sounding stupid I couldn't find the exact reason why this was wrong as the 10mm would take 61amps

could anyone clear this for me?

Why do you say minimum 16mm tails and 10mm bonding?
The minimum size for bonding is 6mm unless PME conditions apply.
There is no lower limit on tail size, other than the availability factor.


Sent from my iPad using Tapatalk
 
What matters is whether the cable complies with the requirements.
As cables with insulation and sheaths, and cables with reinforced insulation satisfy the requirements for double insulation, such cables are deemed as being double insulated.

.

Well if you want to be pedantic then technically speaking an insulated and sheathed cable may be considered to afford equivalent protection to DI subject to some stipulations (which I can't remember) rather than actually being deemed to be double insulated.

Plus reinforced insulation is a separate thing to DI, although the regulations consider them to be equivalent.
 

V/Ze= 766A

I=766
T=0.16
K=143 (not incorporated in a cable or bunched)

766x766=586756

586756x0.16=93880

square root of 93880=306

306/143=2.13mm for your main earthing conductor.

Taking reg 544.1.1 in to account the 6mm bonding conductor is adequate.

Edit: Based on a BS1361 fuse
 
Last edited by a moderator:
V/Ze= 766A

I=766
T=0.16
K=143 (not incorporated in a cable or bunched)

766x766=586756

586756x0.16=93880

square root of 93880=306

306/143=2.13mm for your main earthing conductor.

Taking reg 544.1.1 in to account the 6mm bonding conductor is adequate.

Edit: Based on a BS1361 fuse

Hi Lee or anybody else. Can you confirm what the T value of 0.16 relates to with this calculation?

Thanks
 
V/Ze= 766A

I=766
T=0.16
K=143 (not incorporated in a cable or bunched)

766x766=586756

586756x0.16=93880

square root of 93880=306

306/143=2.13mm for your main earthing conductor.

Taking reg 544.1.1 in to account the 6mm bonding conductor is adequate.

Edit: Based on a BS1361 fuse
Hi Lee or anybody else. Can you confirm what the T with value of 0.16 relates to here?

Thanks
 
The supply authority and utility provider will expect to see 16mm tails and therefore a 10.0mm bond is required to satisfy their requirements also. The regs and calculations can determine other values but to ensure you meet the minimum requirements of the energy supplier this is what I would install as a contractor.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
LONDON (barnet)

Thread Information

Title
10mm meter tails 60amp fuse 6mm bond
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32
Unsolved
--

Advert

Thread statistics

Created
simpson93,
Last reply from
ronalsparks,
Replies
32
Views
13,204

Advert

Back
Top