Why do you say minimum 16mm tails and 10mm bonding?
The minimum size for bonding is 6mm unless PME conditions apply.
There is no lower limit on tail size, other than the availability factor.
Sent from my iPad using Tapatalk
Do you not mean to say 'demand factor' or 'load factor'?
V/Ze= 766A
I=766
T=0.16
K=143 (not incorporated in a cable or bunched)
766x766=586756
586756x0.16=93880
square root of 93880=306
306/143=2.13mm for your main earthing conductor.
Taking reg 544.1.1 in to account the 6mm bonding conductor is adequate.
Edit: Based on a BS1361 fuse
Hi Lee or anybody else. Can you confirm what the T value of 0.16 relates to with this calculation?
V/Ze= 766A
I=766
T=0.16
766x766=586756
586756x0.16=93880
Hi Lee or anybody else. Can you confirm what the T with value of 0.16 relates to here?
The supply authority and utility provider will expect to see 16mm tails and therefore a 10.0mm bond is required to satisfy their requirements also. The regs and calculations can determine other values but to ensure you meet the minimum requirements of the energy supplier this is what I would install as a contractor.
Reply to 10mm meter tails 60amp fuse 6mm bond in the UK Electrical Forum area at ElectriciansForums.net
Hi I don't know if I should ask it here or the main electricians forum. It's about CU change and the work around it and the CU change will be done...
11K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
4K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
6K
Hi all, This week while wiring a very old farmhouse for heaters I noticed the incoming cu tails were very long, around 20 metres from the fuse...