Amp David

-
Mentor
Arms
A 20 amp DP switch is rated to switch a max load of 20 amps right?

Being told this afternoon that they can only be installed on a circuit that is fused at <=20 amps.:whatchutalkingabout
 
im in agreement with you amp. ive used them in the birds mums house instead of a fused spur, to isloate the washing machine, and dishwasher. a standard domestic socket is only rated to 13A per outlet, yet they are often installed on a 32A MCB.
 
disagree. the 20A switch's load is limited to what you connect to it. obviously, you would not connect a load exceeding 20A.
 
so expanding on that. an 80A Main Switch in a CU protected by a DNO 100A fuse is a no no then?
 
So connecting one to a circuit protected by a 30/32 amp fuse or breaker is not allowed even if used as a switch for a single socket ?
 
Surely as long as a load of less than 20A is drawn through that switch, it doesn't matter what the MCB is rated at?

If you were using it as an isolator for a single 13 amp socket for example, you'd be fine IMO.

I've got a 20A DP in my kitchen which isolates the 13A socket for the washing machine under the counter. Doesn't make any sense that this wouldn't be compliant.
 
Last edited:
So connecting one to a circuit protected by a 30/32 amp fuse or breaker is not allowed even if used as a switch for a single socket ?

The units are to BS1363, exactly the same as a twin or single 13A socket outlet.

The switching is rated at 20 Amps.
 
There was a bit of a debate about this very subject not long ago in another thread....
http://www.electriciansforums.net/electrical-forum-general-electrical-forum/38029-grid-wiring-kitchen-ring.html

M
y argument was that if you're feeding a socket outlet that's going to have something plugged in then the plug top will be fused.

Therefore, having a fused spur aswell would be pointless and would lead to discrimination issues as you'd have 2 fuses in series.

I see no point in fusing a 20A switch which is never going to be handling more than 13A.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Amp David

Mentor
Arms
-
Joined
Location
Glossop

Thread Information

Title
20 Amp DP switches
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
Amp David,
Last reply from
Amp David,
Replies
12
Views
24,852

Advert

Back
Top