evening all,

I was told to run 2.5 cable from fuseboard to supply a 3.5 kw single oven. Job is done....

Now they've said theyre going to put in a 5.3kw double oven in.

Question i have is can I apply diversity to this and keep 2.5t+e or do i need to run a new 6mm,

advice would really appreciated

thanks
 
23 amps. Well technically 20amp fuse still exists so the cable is protected subject to normal de-rating considerations. Pushing it a bit IMHO. I think I`d recommend an upgrade in writing so if/when you have to go back to upgrade your covered. Sometimes these ovens have 5.3kw or something on them and that includes 3 elements say 2x grill and 1x rear circular fan element. As its unlikely or impossible perhaps to have the rear fan oven element on at same time as the grill you would be under 20 amps again
 
Last edited:
the diversity allowance for cooking appliances in a household is 10amps + 30% f.l ( full load if i remember right ) +5amps if the cooker outlet has an incorperated socket outlet.
 
which gives around 15A without a socket outlet ( top of head as calculator not to hand). so 2.5mm on 20A is adequate. problem would arise if they added a hob or changed to oven for a higher rated one.
 
just worked it out. 5300/230 = 23A

10A + (0.3 x 13 ) = 13.9A. where did 16.9 come from?
 
1.divide the watts by 230 to give a total load current figure.
2. apply diversity: 10A + 30% of remainder = answer. add 5A if a socket outlet is incorporated.
 
should add here that watch out for old BS3036s...as this affects the CCC of cables....as in for 2.5mm flat T&E on a BS EN 60898=27A....for BS3036=24A.........
 
just worked it out. 5300/230 = 23A

10A + (0.3 x 13 ) = 13.9A. where did 16.9 come from?


are you saying its 30% of whats left of the 23 amps after taking the 10 off? I thought the fl (in the osg) meant full load so 30% of 23 amps (not 13amps) ie 6.9 amps plus the 10
equalling 16.9
 
Last edited by a moderator:
its the first 10A...then 30% of whats left......then if theres a BS1363 outlet incorperated into the double pole iso for the cooker....then just add 5A......
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
5.3 kw double oven on a 20 amp fuse with 2.5 cable
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
58
Unsolved
--

Advert

Thread statistics

Created
egginyourface,
Last reply from
Engineer54,
Replies
58
Views
43,023

Advert

Back
Top