Right, so in an alarm state sounders go off on both zones, why is there two sounder circuits then ?, so for an external sounder I need to go out to that sounder from the board terminals and back again into the sounder circuit cable ends and connect in series or can I double up on the board terms but that would be a parralell connection which is not permitted according to the blurb with the alarm
Pict
there are 2 alarm circuits as more a fail safe and its good design to overlap sounder circuit one with two in the areas to be covered so in the case of a fault blows the pcb fuse of on sounder circuit the other will still give good coverage, ive seen in past systems where a sounder circuit was wired to different floors but this should be now clear that its a poor design as losing one sounder circuit may not evacuate a floor in a fire but covering the floors with sounders balanced over the 2 alarm outputs and overlapping to a certain extent would still alert everyone.Right, so in an alarm state sounders go off on both zones, why is there two sounder circuits then ?, so for an external sounder I need to go out to that sounder from the board terminals and back again into the sounder circuit cable ends and connect in series or can I double up on the board terms but that would be a parralell connection which is not permitted according to the blurb with the alarm
Pict
Is the second sounder circuit possibly used for operating a relay which may inturn operate a phone modem/dialler?