if the supply is TNS then it should not be a problem if you bond the the MET from each supply together. If it is TNCS then i would say no because if you lose the neutral to one incoming supply the current would find a path through all the bonded metalwork and could overload neutral earth conductors on the other supply
 
if the supply is TNS then it should not be a problem if you bond the the MET from each supply together. If it is TNCS then i would say no because if you lose the neutral to one incoming supply the current would find a path through all the bonded metalwork and could overload neutral earth conductors on the other supply

Exactly why you should link the two MET's regardless of earthing system......if you dont the situation you describe would result in a dangerous PD between conductive parts in the same building.....The linking earthing conductor should be sized accordingly.
It's likely that in reality the two MET's will be linked via parallel paths through bonding and cpc's anyway.....better to provide a properly designed copper link in my view.....
 
Last edited by a moderator:

Reply to Bonding between two buildings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
  • Question
Hi all… just after some independent opinions… I have a VM install with 4 units in one building. The VM the engineer ran one cable from the street...
Replies
8
Views
691
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Replies
17
Views
2K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
544

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock