Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted.

No idea what size the incoming fuses are or incoming conductor sizes. Would have to contact the DNO but not sure whether they would give that info to anyone or how long it would take for that matter?

The 200A fuses feed a busbar chamber which we are tapping off with 70mm tails and 35mm earth to feed our DB.

Can our bonding be sized from that - 25mm?

Would 16mm suffice?
 
Can’t really tell as the cable goes straight into the cabinet.
Can you really not see it anywhere?
Nothing to lose by asking DNO what their records say.
Seeing if PEFC and PSCC (phase to N) are similar or wildly different might give you a further clue.

As you probably gathered you need to know whether you are aiming at half the earthing conductor if not PME or according to the table in the regs if PME.
 
investigated a little bit more today and noticed a piece of metal connected externally to the incoming head which was bolted to some copper earth tape going up into the cabinet. The earth tape has a sticker on advising “Earthing Terminal PMS System”

Still couldn’t decipher what size the incoming conductors are as the cabinet is sealed. The armoured feeding the incoming head doesn’t have any conductor sizes marked on it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Newcastle Upon Tyne
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Bonding Size for Old Incoming Supply
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
IAmSparkytus!,
Last reply from
IAmSparkytus!,
Replies
5
Views
1,330

Advert

Back
Top