R

ray1972

I have a question regarding the distribution of single phase 220 VAC branched directly from a 380 VAC 3 phase supply. I have done some research on the web, however have not been able to find a formula that exactly explains my situation, at least not clearly enough to make a solid decision.

I am not experience in the math behind branching 3 phase to single phase, especially when it comes to loads. I asked for 2 separate single phase supplies. One 62 amp and one 32 amp, which will be running 2 separate control systems.

It seems that I have been provided a single 62 amp 3 phase supply, where I have been instructed to tap off the 3 phase to acquire my 2 separate single phase lines. My first concern is that the 3 phase supply will be very unbalanced, pulling 60 amps off one leg and 30 off another.

Just to start, let's say I was balanced across all three branches. Would this be the proper formula to calculate the per line amperage at 220 single phase per leg?

380*1.73*60/3/220

The above formula brings me back to 60 amps per leg, however from what I have seen, adding amps per leg is not typically acceptable.
 
If you’re wanting 63A on one phase and 32 on the other you will have 54A flowing in the neutral. This is given by In = √((L1²+ L2²+ L3²)-((L1*L2)+(L1*L3)+(L2*L3)))
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Branching 3 phase 380 to single phase
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
ray1972,
Last reply from
Knobhead,
Replies
2
Views
2,599

Advert

Back
Top