Evening all.
This has been in the arms for a while now and I meant to post it in the open forums ages ago but totally forgot.
It's the design template I created when I did my C&G 2400 design course (C&G 2391-20 in todays money). I have tweaked it a bit to update it, regs references etc but the fundamentals haven't changed at all.
Hope you find it useful.
:cyclist:
Thanks Lenny.
It would be really handy as a spreadsheet :wink_smile:
Funny you should mention that.
I started one, ages ago with hyperlinks to actual regs pages etc, and never have got round to finishing it. Who knows, maybe one day.........got this HNC thingy robbing me of all my spare time at the mo though.:smart:
always looked for one of these when didnt quite grasp it all... whats point 7 all about, would you max zs from circuit breaker??? cheers will save it anyway and print and pass on too i think appropriate
Point 7 is calculating wether or not the CPC would be large enough to cope with the magnitude of earth fault current that may flow under fault conditions, using the adiabatic equation.
so you would use, the breaker device max zs for the sum...... would you multiply by 0.8 before you find your fault current??? ;) )
no mate you wouldnt, asitsthe max fault current you are looking for, to ascertain if your protective devices have sufficient breaking capacity to contain the fault.
ok so point 7 is very clear in saying, thermal constraints i.e breaking capicty for that point ic circuit... i thought when done at the origin and devices selected along with this it would cover downstream ones as got less fault current....
but i think i know you still need to check when out in industry , where im on about domestic lol
what your talking abput mate is called cascading, or back-up protection. It is permitted in industry too.
what usually happens is that you have a main board, that will be weither MCCB's or fuses, this will then feed smaller panelboards, or large machines. The panleboards will have MCCB's or fuses, and then your final ccts will be fed from a 3phDB that will be on MCB's.
this is because its very difficult to acheive discrimination with MCB'as feeding MCB's, but easier to use fuse's or MCCB;s to feed MCB's.
you will then in all likelyhood, if using large cables to feed you final 3ph DB, be using the MCCB or fuse on the feed as backup protection for short circuit and/or earth fault protection.
i do think it should say at point 7 , Uo /Ze.... but im sure there is perfectly good reasn why... dont mind me
I suggest you investigate exactly what the adiabatic equation is and how it used in circuit design.
so does that mean you would use the max zs reading of the breaker for the design???? sorry
No, the permitted device Zs doesn't come into the equation. The value used is the calculated theoretical of circuit Zs found by using the formula Zs = Ze+(R1+R2).
This theoretical Zs value is then used in a calc with the supply voltage to find the (I) component (which is the maximum earth fault current that could flow in a fault condition) of the adiabatic equation which is - S = sqroot of I squared x t divided by k.
The use of this equation with the correct information will then confirm wether or not the CPC of the proposed circuit is large enough to cope with the fault current that may flow in it.
For step 6, would you take 80% of the Zs AND multiply the R1+R2 by 1.2? I thought it was one or the other?
I have been asked to connect a mobile home on a large transport site. The supply cable run is approx 250 meters. When I try to work out the voltage drop for the swa cable from size 25mm upwards there are three values in the regs book x,y,and z which shoul I use
Thanks anybody
Thanks anybody
Upto 35mm, I continue to use the resistive (r) component for calculating the VD. By moving to the impedance (z) component you will end up with a pessimistically large conductor size.
Going above 35mm and bringing reactance & impedance in to play makes it all a bit more complicated as power factors (if known) and temperature corrections come into play.
Have a read from page 312 (new green book) onwards (appendix 4).
I can provide everyone with a excel automatic caluator butit is not a valid file extension to upload!!!
is that maximum allowable earth fault current is 1mA?
sorry i dont understand about Cg, Ci, Ca.....
thank you
Excellent, been meaning to knock one of these up for the back of my regs manual but aint had the time. A handy must to have a hard copy like this, especially the adibatic equation if you looking to save a few £££.. Why go large if theres no need!
Cheers
I like it JUD. I didn't see anything about ring final circuits though, or thermal withstand calcs for short circuit protection.Very good template though.
I like the clear layouts of both Lenny's and JUD's cable design templates
Just a couple of points
I would use U and Uo for the 3-phase and single phase voltages, respectively
JUD you have forgotten, in step 6, the Length of the final circuit being calculated.
Otherwise excellent stuff !
thts brilliant len, thanks
In step 6, do i have to multiply it by 0.001 to get ohms? i.e 4.91mohm/m x 9 metres x 1.2 x 0.001 = 0.053 ohms?
Or have i got it confused with something else, cheers mate
Yep or divide by 1000 (4.91 ÷ 1000) x 9 x 1.2 = 0.053Ω
It's all the same thing.
Brill but defo needs the spread sheet version! Thought it was the answer to all my prayers then :juggle2:
Hi, I'm interested in seeing this spreadsheet as I'm doing cable calc's, trouble is all these books and tables are Blowing my mind. Can't seem to open it tho !! Any ideas ???
Hi
Where is the template from post #1, I dont see it.
Also, how do I contact Guest 123 to ask him for a copy???
Thanks.
Cable Calc Template.
Guest123,
Mark.W,