My job ended at installing the ring main and spurs. When he asked about installation of mats and I gave him a price he said tiler would do it. I'm just going to go in check my spur connection and tell him it's down to the tiler to sort as he has installed and I have installed wiring capable of handling the load. Sometime being too helpfull or kind back fires. Thanks

Hum, so can the tiler do the Part P notification??
 
That's for the homeowner to find out. I did my job and gave certificate. Plus have installed quite a few heat mats and never had any problem before.
 
That's for the homeowner to find out. I did my job and gave certificate. Plus have installed quite a few heat mats and never had any problem before.

You are missing out on jobs if you're happy to quote for fused spurs for u/floor heating then not getting the connect and test work.
 
Phone the manufacture and ask the what the resistance is per meter for that model. Take a reading and see if the element is within their guide lines, if not this can now become very expensive. There is a company that specializes in mobile xray machine that they scan the floor to locate a damaged bit of cable on the under floor heating. I think their prices start at £800!!! Some times its worth it, locate damage and only take up one or two tiles and not the entire floor.

In your case I would only accept responsibility for up to the fsu and not beyond if you did not install it.
 
As others have said, check what the manufacturer's resistance readings were (they will have been supplied with each mat) and ensure that's what you are getting on site. If not then it's likely that the one with the reading that's out is damaged. Also, check if a floor sensor has been used and if so, where it has been located.

As for the load on your circuit, just calculate from the resistances in parallel and compare this with the ccc of your cable for the method of installation.

Remember, all this checking should be paid for by the tiler - you appear to have done what you were asked to do (but learn the lesson about fixed loads on a RFC).

Regards,
 