johntom

Hi
i've been to look at a job today that involves power and lighting to a brick outbuilding (my first outside job). The outbuilding is 1 meter from the main house. There is already a 2.5mm cable coming through the main house wall at a height of 7' which then goes into the outbuilding for the socket (accross the 1 meter span). Is this acceptable or do i need to replace with swa or should/can i use 2.5mm in conduit etc?
 
Agree with notabrightspark.Add a fused spur for the lighting and remember to change the fuse to a 3 amp
 
Hi
are you saying that you can use 2.5mm from the CU to the outbuilding then (via a 3amp fused spur) power the lighting circuit in addition to the radial ( all from the 16amp in the cu) or am i miss reading this?
I had proposed to run a 1.5 and a 2.5 from separate mcb's for the 2 circuits.
thanks for you help
 
Last edited by a moderator:
Are we forgetting earth leakage protection here ????????????????????????????
 
I would suggest running the 2.5mm from the house to the outbuilding in a conduit, or change it for swa to offer mechanical protection, protect using an rcd from the property. Install seperate c/u in outbuilding comprising of 16a radial and 6a lighting, only need mcbs in outbuilding.

Or you can give them my number and i will have a look at it for them, having to explain a job like this on here fills me with dread every time, are you a member of any organinsations niceic etc
 
Hi
yes i'm a member of an organisation and yes i fully understand the procedure you have highlighted. I was just interested in the post about using the fuse spur with lights and power as it seemed to suggest running them both from 1 supply. Forums like this are a helpful learning tool for many people - i am sure you had to learn !
 
If you are getting paid to do a job do it right, 4mm Swa to a 2 way splitter then run your lights from a 5a mcb and your socket from a 20 and protect them with a 32 amp mcb from the house.
 
If you are getting paid to do a job do it right, 4mm Swa to a 2 way splitter then run your lights from a 5a mcb and your socket from a 20 and protect them with a 32 amp mcb from the house.
He maybe on a budget and i don't see why as the 2.5 T&E is already there in the outbuilding he can't utilise that.;)
 
If there are any mettalic pipes or other extraneous conductive parts [metal structures in contact with the ground],then the minimum size cable will have to be 10mm2 ,unless you TT the installation in the outbuilding.



spark1
 
If there are any mettalic pipes or other extraneous conductive parts [metal structures in contact with the ground],then the minimum size cable will have to be 10mm2 ,unless you TT the installation in the outbuilding.



spark1
Why would you do that.The Op stated that the building is only a metre away from the house.Personally it doesn't need spiked and i would use the existing cable for the power and lighting by adding a spur for the lights:cool:
 
Granted there is a 2.5mm there at the moment, but is it protected? open to the elements? if its a job and he wants to get repeat business he should do it in Swa. I accept it might be more costly but wait till the homeowner gives him hassle when the cable fails due to being exposed to the elements
 
Granted there is a 2.5mm there at the moment, but is it protected? open to the elements? if its a job and he wants to get repeat business he should do it in Swa. I accept it might be more costly but wait till the homeowner gives him hassle when the cable fails due to being exposed to the elements
If it's only feeding 1 socket,i'd pull the cable back to the point of exit from the house and put it in pvc conduit.:D
 
Macca . the outbuilding is remote from the existing main building.....be it 1m. or 100m. therfore if it is to utilize the existing fault protection of EEBAD [ADS],then the equipotential zone extends to the outbuilding which means 10mm2 bonds to any extraneous conductive parts whithin it. Alternatively the outbuilding can form its own equipotential zone by creating aTT system.............if no extraneous conductive parts then no problem !


spark1
 

Reply to Cable to outbuilding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock