Just a quick one! I believe this time delay switch should work for my old panel heater (1.25kwh) because it handles loads up to 16A. Can anyone confirm this for me? I had someone tell me I needed a fused spur switch but others tell me I don't.

FYI: the aim is to ensure the panel heater turns off automatically after 15 mins to stop guests leaving it on all day and all night.

Thanks guys.
 
you should fit a 13A fused connection (FCU) preferably D/P. this protects the cable after the FCU as it is musy likely not more than 1.5mm (max. 19A). your RFC ( if it's on a RFC) will be protected with a 32A MCB. also you have convenient local isolation.
 
you should fit a 13A fused connection (FCU) preferably D/P. this protects the cable after the FCU as it is musy likely not more than 1.5mm (max. 19A). your RFC ( if it's on a RFC) will be protected with a 32A MCB. also you have convenient local isolation.

To be clear, you’re saying I could use that particular switch but it’s preferable to have fused spur?
 

Reply to Can I use this Time Delay Switch on a panel heater? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
629
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
978
I don't know if you are sorted yet but I would only do the single supply option as a very last resort. Great care has to be taken in setting up...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top