Found what this board SHOULD look like. I'm just wondering if I should just get one of these, rip the inards out of both, and put the inards of this one into the one in the wall, and not faff about trying to rewire or understand the mess.
Is that an official 'publicity' shot? If so and that's the best they could get things to fit then that's not a great advertisement - worse than the MK lean!

Might well be the best way to resolve what's there given the limitations of replacing it... Though some RCBOs for at least some circuits sounds like a good idea too.

If that's difficult (not sure what their availability of Type A stuff is), then (Tin hat time) - other than perhaps not being able to rely on 16kA breaking current - are there really any risks in replacing it all with another brand of matched switchgear that has been type tested together - I doubt the enclosure it is in makes much difference in terms of safety...
 
Is the second rcd still there somewhere, or has it been binned? Id have no issue with crimping the tails with a hydraulic crimper and heat sleeve, and refitting the second rcd and putting it back to standard, but remember the downstream mcbs shouldn't exceed the rating of the rcd anymore if its got a bigger main fuse in, and really we all ought to be fitting type A rcds too now (can't see what type that one is) personally I'd have the whole thing in the bin and start again.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Can you extend meter tails inside a consumer unit ?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
vwes59,
Last reply from
suffolkspark,
Replies
21
Views
11,869

Advert