O
Octopus
I think this one is c1.
Done 3 months ago.
No paperwork.
View attachment 36531
View attachment 36532
View attachment 36533
What is the C1?
I think this one is c1.
Done 3 months ago.
No paperwork.
View attachment 36531
View attachment 36532
View attachment 36533
you asked what code ?TN S. No signs of damage. I'm not doing an EICR just installing outdoor lighting.
Only recently - it was prohibited until a handful of years ago.Yet a seperate cpc can enter a separate hole if ran in parallel with a swa
C1 for no blanks - Direct access to live parts.I think this one is c1.
Done 3 months ago.
No paperwork.
Presumably the missing blanks giving access to live parts.What do you think would warrant a C1?
also there is only 1 10mm bonding cable from MET block which would mean only 1 bonding cable running to incoming gas or water
Or even to both via one cable![]()
I was taught to run 1 to water and another to the gas from the MET.
Standard finger -if you can poke something 12.5mm in dia and 75mm long and touch and exposed part then it needs to have a gromit/ gland fitted.
I remember my collage lecturer finding a standard finger amusing. I don't know why?![]()