As it says - what code should I be giving to a metal CU where the cables come straight in through the knockouts without any form of protection. Meter tails and main earth enter through different apertures 'n all.
Discuss Code for lack of grommets/glands in Amd 3 Consumer Unit. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Whilst I agree that in reality it's unlikely to pose any real issue in a domestic installation I would still C2 it as it is not something which I would condone.the different holes i'd code as C3 as the small eddy currents on a dom. will not cause a problem
C2 potentially dangerous?Whilst I agree that in reality it's unlikely to pose any real issue in a domestic installation I would still C2 it as it is not something which I would condone.
It does have the potential to be dangerous, although as stated with the loads in a domestic installation this is unlikely.C
C2 potentially dangerous?
The earthing conductor must pass through the ferromagnetic enclosure together with the live tails. I'm not sure if that was what you were asking though.Is the main earth a"tail" ?
no blanks as wellI think this one is c1.
Done 3 months ago.
No paperwork.
View attachment 36531
View attachment 36532
View attachment 36533
Are the tails insulated and sheathed?
Is there any signs of damage /abrasions to the tails?
And is it TT?
I think this one is c1.
Done 3 months ago.
No paperwork.
View attachment 36531
View attachment 36532
View attachment 36533
you asked what code ?TN S. No signs of damage. I'm not doing an EICR just installing outdoor lighting.
Only recently - it was prohibited until a handful of years ago.Yet a seperate cpc can enter a separate hole if ran in parallel with a swa
C1 for no blanks - Direct access to live parts.I think this one is c1.
Done 3 months ago.
No paperwork.
Presumably the missing blanks giving access to live parts.What do you think would warrant a C1?
also there is only 1 10mm bonding cable from MET block which would mean only 1 bonding cable running to incoming gas or water
Or even to both via one cable
I was taught to run 1 to water and another to the gas from the MET.
Standard finger -if you can poke something 12.5mm in dia and 75mm long and touch and exposed part then it needs to have a gromit/ gland fitted.
I remember my collage lecturer finding a standard finger amusing. I don't know why?