Update.
Sorry I did not say in my post, but I noticed the incoming supply at the same time as the electrics were done, the electrician who changed the CU was aware of the incoming cables and the state they were in.
I did ring the DNO, Northern Powergrid, I explained on the phone about the cables being bare, they asked me to email pictures (the exact ones I posted on here) within 45 minutes someone came out to look at them, within 2 hours of that, they (DNO) were digging up the garden and replacing it, So it has been replaced.
The old box on the outside wall has gone and there is a new cable coming up the existing pipe and connected into the existing cable which is clipped in the photo horizontally. Have photos if interested!
The property was built 1946, my grandmother had some electric work done in early 1980s (don't know what though) but nothing since then.
When I had the central heating system installed back in March, the electrician who wired the boiler fused spur did mention something along the lines of there is no earth! and mentioned something about a ''PME'' (I could have that wrong), but he said i need the dno to provide an earth.
What he did do is he said he will run a bond which he said is not ideal but better than nothing. After he finished I looked and he ran a 10mm earth bond from the water pipe inlet up the wall capped, through the ceiling, under floor upstairs and down in to old consumer unit, The water never had an earth bond, the property never had gas until March this year.
If you look in the photos of what the electrics were like before the CU install, you can see the temporary earth coming through the ceiling originating from the water pipe.
So from all that I take it the property has never had a connection to earth and possible still doesn't if he has done it incorrectly, do I need to check with the DNO to see if its capable of being run the way he has it?
The guy who installed the CU did bond the gas by piggy backing the bond clamp on the water pipe near by.
Definitely interested in some photos of the new install!
As others have said, it appears that the consumer unit is not the main issue here.
It's likely if they have put a new install in that it is PME capable (which means that an earth could be run as it has been). However, the key is that ONLY the DNO can decide and do that.
It is probably a good idea to contact them again and explain and ask for an earth safety check. They may be able to confirm that the earth is acceptable as it is, and will do it correctly with their labels and an earth terminal.
There are ways to test whether PME is possible/effective, and the electrician
may have done that, but it's still not within his remit to decide to change it.
That doesn't make what is in place now unsafe necessarily - though the readings on the certificate will be helpful in deciding that.
It appears that you've been let down by two electricians here.
The first one who did the boiler should have either contacted the DNO themselves or got you to do it, and had them in to see if they could upgrade the earth - at that point I expect they would have noticed the outside cabling and arranged for it to be changed.
The water bonding was necessary as well, so not a waste that he did it, just that it was not an acceptable alternative to a proper main earth. Do you know the if gas has been bonded now too?
The second electrician should not have done
anything with the outside cable in that state - they should have called the DNO themselves as an emergency job and waited for it to be fixed before proceeding. They should absolutely not (if they did) have connected the earth up as they did, even if tests suggested that the install was PME.
Now that the new supply is installed, the good news is that it is probably not a huge amount of work to get things into an entirely satisfactory state. It seems like what you need is a competent electrician to oversee ensuring everything is as it should be - and maybe the one who does the EICR could be that.
I would find a few from the NAPIT or NICEIC site that are rated to do EICRs, and contact them for a discussion/quote, but explain the situation. You sound like you have a good enough grasp of the issues now to be able to spot those who do not give good clear answers as to how they would proceed.
Sadly as you've found, ensuring they have membership is not the guarantee it should be.
Not sure if any of the forum members are close to Bradford and willing to assist, or can recommend someone who is reliable and competent.
It may also be worth contacting NAPIT, I am told they have a rather better approach to maintaining their standards than some, so they may be able to assist. Usually, they ask that you go through a complaints procedure with the electrician first, but in this case, if you show them the pictures (or direct them to this post), they may be willing to take a more proactive approach. If I was a NAPIT member, I might even raise it myself with them as a poor example of the "brand" that I was paying for the privilege of representing.
In terms of price for an EICR, it's not always a good guide - You should be able to get a perfectly good EICR for less than £200. I would avoid national firms who specialise in EICRs as they have a habit of fitting in as many in a day as they could and barely scraping the surface.