What do you think would warrant a C1?

Which certs are you using? The ones in BS 7671 don't have a check list!
 
Access to live parts a major issue on that installation by not fitting blanks, Knockouts with no glands and tails showing signs of damage. Tail gland kits are not expensive and make such a neater looking job. The MET appears to have a 16mm from DNO cut out to MET block then a 10mm run into the consumer unit, also there is only 1 10mm bonding cable from MET block which would mean only 1 bonding cable running to incoming gas or water? the lack of labeling on the CU and MET also shows signs of a cowboy installer grab the cash and run jobby to me.
 
also there is only 1 10mm bonding cable from MET block which would mean only 1 bonding cable running to incoming gas or water

Or even to both via one cable ;)
 
I was taught to run 1 to water and another to the gas from the MET.

Then your teacher was correct,both services sometimes require bonding, running a cable to each can cover that requirement
there is however,more than one way to skin a cat :) and because something is done correctly,it does not mean there are not other permitted means to comply

Quite a lot of electrical requirements can be achieved with differing solutions, it can be elusive sometimes finding justification for another persons method

I suppose that is why electricians are regularly disputing or interpreting regs with one and other,they can have differing and compliant means to reach the same outcome
 
Exactly why i love this trade i learn new ways all the time. My boss would always want me to install separate bonding to incoming gas and water and thats what he prices for so i do as he says, but every spark is different and as i say im learning all the time and loving it.
 
Standard finger -if you can poke something 12.5mm in dia and 75mm long and touch and exposed part then it needs to have a gromit/ gland fitted.
I remember my collage lecturer finding a standard finger amusing. I don't know why?:rolleyes:
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
South East
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Code for lack of grommets/glands in Amd 3 Consumer Unit.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
South Spark,
Last reply from
Paul228,
Replies
30
Views
18,238

Advert

Back
Top