Hi, recently changed ccu from rewirable too modern dual rcd type. No probs with test results etc, only prob gas and water bonded with 6mm, wiring in old colours etc. But customer does not want walls ripping too bits too solve . Should i use EIC and put these items in (departures from bs7671) or PIR and give items the correct codes. thanks
 
Aico 3000 Range
This official sponsor may provide discounts for members
Advertisement - Content continues below
B

Bane

  • Thread Starter Thread Starter
  • #2
*Throws this back to the top of the pile*
 
C

Carter

  • Thread Starter Thread Starter
  • #3
Poking around the red book I find reg 131.8

Additions and alterations to an installation

No addition, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the RATING AND CONDITION of any EXISTING equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, SHALL BE ADEQUATE.
It can also have implications for things like the dispensing with supp bonding in bathrooms which requires that the main bonding is fully up to scratch.

Have you got <0.05 ohms for each of them? not actually sure of the technical reasons for the BS7671 increase in bonding conductor size (has there been a rise in expected P.E.F.C.s?) but if they satisfy the 50 miliohm requirement why change them out.
 
E

EasyFox

  • Thread Starter Thread Starter
  • #4
Leave bonds as is, make a note in the deviations comment box on cert (not ideal but hey what can you do).

Supply customer with a letter/dissclaimer about undersized main equip bonds,
(could also give them a print off of the niceic bonding leaflet, they may say do it then ;))
You get customer to counter sign a copy of the letter & file it with the cert.

You have to issue an EIC, periodic is not the one to use for the installation of a cu.
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Consumer Unit Change. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Aico 3000 Range
This official sponsor may provide discounts for members
Advertisement - Content continues below
Top Bottom